Old 09-10-2009, 07:37 PM   #1
Wink
Goodman 4 flashes on control board
I have a 10 year old Goodman GMP Heating unit.
ICM Control board m/n: B18099-06
AC works fine.
This is what happens with the heater:
Inducer motor comes on
light gets lit and all burners come on
I hear relays clicking on the ICM control board, but the heater blower never will come on. Few minutes later it kicks off because it gets to hot then flashes the 4 blinking lights indicating open limit because of the temp. without blower.
Please help with your suggestions. Is it the control board?
r.
BRad
bigmac71201 is offline   Reply With Quote
Old 09-10-2009, 09:06 PM   #2
HVAC / Plumbing
check the terninal on the board with v m that supplies power to the blower motor
kenmac is offline   Reply With Quote
Old 09-11-2009, 12:07 PM   #3
I get 120 volts to cool fan on blower when calls for ac.
I do not get any voltage on heat fan blower when calls for heat.
Old 09-11-2009, 12:24 PM   #4
Hvac Pro
You need a new board and there has been problems with those boards. The new board may be a retrofit so read the instructions carefully.
Old 09-11-2009, 07:58 PM   #5
Senior Tech.
Ten year old GMP. Better get a pro to inspect the heat exchanger's crip rings.
Milk man is offline   Reply With Quote
Old 09-12-2009, 12:34 PM   #6
thanks for the quick reply.
Ordering board today and hopefully will resolve the issue.
Old 09-28-2009, 03:53 PM   #7
Thanks for the advice...
I replaced the control board and the problem has been resolved.
r/
Brad
Carrier furnace control board - OEM or ICM ? anku HVAC 13 10-12-2012 11:50 PM
Goodman Circuit Board Shot - Can I Jury Rig Fan? ChrisInAtlanta HVAC 2 08-03-2008 03:54 PM
Blower control board mlmaher HVAC 1 11-24-2007 02:39 PM
Ruud a/c control board replacement ? kourso HVAC 1 07-20-2006 10:33 PM