I have a new home and recieved a Honeywell IAQ (YTH9421C1002) from a family member who works at Honeywell. The furnace installer did not know how to install the IAQ with the furnace so put his own thermostat on. The Gibson(Nordyne) furnace is a SC92 and has the following connections:
R
C
Y
G
W
the AC is hooked up to C & Y.
I am able to get the furnace to run, but not the humidifer which only needs a 24v red wire/white wire to turn on the solenoid valve. I don't want to post what I wired to skew any answers.
Thanks in advance
12-07-2010, 06:05 PM
#2
Professional
just to verify you are not using iaq stat? What model humidifier? DO you have a humidistat?
IT IS WHAT IT IS To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts.
12-07-2010, 06:45 PM
#3
I do want to use the IAQ stat since the original one didn't have humidity control built it.
The humidifer is a Skuttle 2100
12-07-2010, 06:59 PM
#4
Professional
Do you have the control module from the stat wired at all?
12-07-2010, 07:03 PM
#5
Yes, I have the honeywell stat wired to 123 on the equipment control module
12-07-2010, 07:08 PM
#6
Professional
ok. do you conventional A/c or heatpump
12-07-2010, 07:10 PM
#7
conventional a/c
12-07-2010, 07:11 PM
#8
Professional
one more question.... outdoor sensor or no? and does humidifier come with a transformer?
12-07-2010, 07:18 PM
#9
yes there is an outdoor sensor, and the humidifer doesn't have a transformer, unless you use the humidistat that comes with it, but I want to use the Honeywell stat instead.
12-07-2010, 07:22 PM
#10
Professional
G/F-------------------- C/M------------------------ A/C
R-------------------------R
C-------------------------C--------------------EITHER WIRE FROM A/C
W-------------------------W
G--------------------------G
Y--------------------------Y-------------------EITHER WIRE FROM A/C
hum1 to
r right above it
hum2 to solenoid valve
C also to other side
of solenoid valve
out1 and out2
to outdoor sensor
Preferably it would be hooked up differently using a 20va transformer to provide power for the hum. this would ensure that you were not robbing power from the furnace which on some furnaces has caused problems
I have this stat and install this stat all the time, I LOVE IT!!!!
let me know if you need help with the setup functions
12-07-2010, 07:27 PM
#11
What about the jumpers on the module
R to RC to RH?
12-07-2010, 07:30 PM
#12
Professional
leave them
The Following User Says Thank You to hvactech126 For This Useful Post:
12-07-2010, 07:58 PM
#13
The furnace kicked on(which is good considering it was -2F this morning). I can't tell about the humidifer right now, but I'll update on that. Thanks for your help!!!
12-07-2010, 08:11 PM
#14
Professional
in setup you only want the hum to run with the furnace. also you can check operation by going to the test function in setup
12-08-2010, 08:17 AM
#15
The humidifer doesn't seem to be working. I have one of the solenoid wires to C on the module, and the other to hum2, and hum1 jumped to RH. I may check the valve, by wiring 20v straight into it.