Gas Furnance Over-firing, How Do I Correct? - HVAC - DIY Chatroom Home Improvement Forum
Old 09-15-2010, 03:29 PM   #1
Seasoned DIYer
Rewards Points: 150
Gas furnance over-firing, how do I correct?
Got a new furnace, and my checking shows its over-firing by about 25%.
Called Northwest Natural Gas. I'm told the energy content is ~1020-1040 BTU/ft^3
The furnace is rated 60,000 BTU input, and there is a section about checking furnace input and there's a chart that shows at 1040BTU/ft^3, it should consume a cube in 63 seconds.
It's consuming it in 50 seconds, so its seriously over-firing.
The installer just hooked it up, didn't do anything with the gas valve.
Does this need to be corrected? Is this within the range that's correctable using the pressure adjustment?
HVAC_NW is offline   Reply With Quote
Old 09-15-2010, 05:22 PM   #2
HVAC / Plumbing
The manual states, at 1040BTU/cu.ft, it should consume a cube in 63 seconds. It's consuming it in 50 seconds, so its seriously over-firing.
If all the installer did was to '' hook it up '' you need a new installer. How did you check it to know it's over fired ??
kenmac is offline   Reply With Quote
Old 09-15-2010, 05:24 PM   #3
An old Tradesmen
Rewards Points: 7,376
What is the gas companies BTU per cubic foot value?
Are you sure its not 950 BTUs per CF of gas.
Yes, that is correctable with a gas pressure adjustment, and a temp rise, and CFM check.
Old 09-15-2010, 06:32 PM   #4
Seasoned DIYer
Rewards Points: 150
I know the energy content of gas, because, I called the gas company. They said it varies from month to month, but its in the range of 1.01 to 1.06 in the last year or so.
Old 09-15-2010, 06:43 PM   #5
HVAC / Plumbing
is this the formula you used ?? 3600 x the dial size (1/2, 2ft, etc,) divided by seconds per revolution .add 10% more for 2# system. Don't know if you have 2 # gas systems there or not
Old 09-15-2010, 06:45 PM   #6
Seasoned DIYer
Rewards Points: 150
Once you know the energy content of the gas, and you measure the cubic feet going into furnace, that alone is enough to calculate the BTU input.
Northwest natural gas says user end of gas is at 6.5" W.C.
Old 09-15-2010, 07:03 PM   #7
Hvac Pro
yuri's Avatar
Rewards Points: 2,286
Did you repeat the test at least 3 times? Gas meter dials sometimes stick and jump a bit so getting it down to a second or 2 is difficult. Let it go round 2X and divide the time by 2 for more accuracy. The installer should check the manifold pressure. It may be overfired from the factory. Have never seen one need new orifices. You don't live in a high altitude area do you? May need de-rating if you do. Check the rating plate for that info.
Old 09-15-2010, 07:14 PM   #8
An old Tradesmen
Put your manometer on it, and see if 3.2" gets your were you need to be.
Old 09-15-2010, 09:28 PM   #9
Seasoned DIYer
Rewards Points: 150
Meter moved smoothly. I measured four cubes, divided by four
Old 09-15-2010, 10:09 PM   #10
Call the installer back out and have him check both the line pressure and manifold pressure. That should be part of any furnace start up because regulators and gas valves are not always set correctly.
Old 09-15-2010, 10:15 PM   #11
Seasoned DIYer
Rewards Points: 150
Old 09-16-2010, 12:35 AM   #12
Do you have an agreement on paper that shows a warranty?
hvaclover is offline   Reply With Quote
Old 09-16-2010, 02:25 AM   #13
Seasoned DIYer
Rewards Points: 150
Old 09-16-2010, 02:32 AM   #14
You should really consider changing your screen name. Your gonna give the PROs the impression you are a tech and will either ignore or hammer you for asking elementary heating questions.
But tell me about the written agreement. What does it say...leave nothing out. Post it if you can.
You have rights as a consumer and I don't like when nice folk like you might be getting screwed.
Old 09-16-2010, 08:20 PM   #15
Seasoned DIYer
Rewards Points: 150
I got the install tech to come back with a manometer. Manifold pressure was pushing 5" WC. Valve manual says factory default is 3.5" WC. I'm not sure how it was this far off. Clocked with utility meter and it appears to be in spec now. I don't think the upper limit for that valve even goes to 5". I don't know WTF happened here.
It's not quite heating season yet. Glad I caught it before it got used beyond testing.
Tags
btus , furnace , heating values , natural gas , pressure regulator valve
Quatro Mba 080 NH2R furnance manual wolfden13 HVAC 1 02-10-2010 04:26 AM
Furnance question. diy4life Building & Construction 29 12-01-2009 05:39 PM
Furnance question satz HVAC 8 02-05-2009 07:44 AM
How do I pick the correct coaxial cable? fwmcbigfoot Home Theater 1 12-30-2008 09:45 AM
Furnance burner won't stay on. 2007ken HVAC 11 03-03-2008 11:29 PM