Old 10-15-2011, 10:13 AM   #1
Gas Furnace Ruud Super Quiet 80 ignition problems
This furnace is a RUUD 2005 model UGLO-07EAMER. It has been having this same problem for the two years that I have owned this house. It works fine, until one day it will not start. One light is on and one is flashing. A technician came out 9 months ago and could not find anything wrong because it decided to work when he was here, then he shook some wires and the furnace came on and off, like there was a short, so he crimped the wires better and then it started up and worked fine. Last week it would not start in the morning but 2 hours later it did. Today it is not starting again. It has a clean filter and no vent restrictions.
Elsinore is offline   Reply With Quote
Old 10-15-2011, 11:25 AM   #2
Professional
check the diagnostic flow chart to identify what the diagnostic flash code LED means
IT IS WHAT IT IS
hvactech126 is online now   Reply With Quote
Old 10-15-2011, 11:36 AM   #3
The power led is on steady..the status led flashes and goes out...chart says to check for 24 vsc from W on IFC. to C.
Check wiring. check presure switch.
Old 10-15-2011, 11:42 AM   #4
Professional
where is the noise from? you have to hunt this down. We cant do it for you over the internet.
IT IS WHAT IT IS
Old 10-15-2011, 12:39 PM   #5
I found out that the noise is a circuit that clicks when the furnace comes on or shuts off.
Old 10-15-2011, 12:48 PM   #6
Are there any parts that I can clean, which may make the furnace work?
Old 10-15-2011, 12:56 PM   #7
Professional
not from the sounds of your problem, no.
IT IS WHAT IT IS
Old 10-15-2011, 01:01 PM   #8
Experienced
Jackofall1's Avatar
Sounds to me like you could have a bad connection on the inducer fan pressure switch or the switch sensing tube has moisture in it, or the sensing tubing loose, or the switch itself is bad.
Mark
Old 10-15-2011, 01:05 PM   #9
I will take out the switch then and replace if can find the switch, where would it be in the furnace?
Old 10-15-2011, 01:14 PM   #10
Experienced
Jackofall1's Avatar
Well looking at the manual for the furnace it appears to be just left of the inducer fan, its a round molded plastic switch with a plastic or rubber hose running from it to the inducer fan discharge.
http://globalimageserver.com/fetchDo...2-52c6c8224436
Mark
Old 10-15-2011, 01:19 PM   #11
What is the name of the switch so I can ask for it at the parts company?
Old 10-15-2011, 01:21 PM   #12
Experienced
Jackofall1's Avatar
Inducer fan pressure proven switch, at least that is what I call it.
Looks like
Mark
The Following User Says Thank You to Jackofall1 For This Useful Post:
Elsinore (10-15-2011)
Old 10-15-2011, 02:29 PM   #13
I took the hose off and cleaned out the hole where the tube goes into the fan with a paper clip, and the hose had a small damaged spot so I taped up that. It is now working, so maybe I will not have to replace the switch, but it has worked before and stopped so I will just have to see. Thanks much for the help.
Old 10-18-2011, 10:47 AM   #14
This morning the furnace trys to start but will not blow hot air.
Old 10-18-2011, 11:01 AM   #15
I'm Your Huckleberry
Is the induer fan coming on? That's the little fan that exhausts the burned gases out through the exhaust flue pipe through your roof, has the little hose attached between it and the pressure switch.
Doc Holliday is offline   Reply With Quote
Ruud Furnace issue grubslinger HVAC 16 09-14-2011 01:13 AM
Perplexing problem, Ruud furnace jbarker HVAC 43 01-20-2010 01:03 PM
Furnace Problems? MCSE HVAC 10 12-20-2006 12:06 PM
Furnace Problems? Part 2 MCSE HVAC 9 11-30-2006 10:25 PM
Intermittent gas furnace problems dcoz HVAC 1 01-16-2006 10:22 PM