Control unit on side of furnace is a Honeywell R857D.
customer.honeywell.com/techlit/pdf/60-0000s/60-2171.pdf
I have a 4 wire setup.
W on my thermostat is connected to C on this unit.
G to G, R to R, Y to Y1.
There's a manual switch on the side of the plenum and and W really goes from the thermostat into this switch then back to C on the control box.
There is about 25 V between C and R with the thermostat not connected.
Now I must be dense but it looks to me like shorting together T and "W" does exactly that. Creates a short on the secondary windings of the transformer. I must be missing something.
raleighthings is offline   Reply With Quote
Old 12-18-2011, 07:18 PM   #17
Limited Experience
R and W (not T and W)
Old 12-18-2011, 07:24 PM   #18
retired elect/hvac/plumb
plummen's Avatar
Location: south east of omaha/The island of misfit contractors
Rewards Points: 2,020
can you post a picture of the low voltage at furnace for us?
plummen is offline   Reply With Quote
Old 12-18-2011, 07:41 PM   #19
Limited Experience
Pics are hard. From my iPhone to another computer just now is a PITA due to several factors. Figure 6 is similar to my setup. Now I realize that what is called Heating Control on that figure is what I have but wired in ahead of the control box. (In a very ugly splice I might add.) I need to go look at it and see what's up inside of it. It is a push button box that is labeled push for manual, pull for automatic. If I push the fan runs but no flames light. I'll be back.
Old 12-18-2011, 08:21 PM   #20
Limited Experience
This "box" is the limit switch. So how can I bypass or test it to see it this is the issue?
Old 12-18-2011, 08:24 PM   #21
Limited Experience
Side question. What gauge wire should be used on the low voltage side of things? What's there now looks like it was done with scrap found in the back of a pickup truck.
Old 12-18-2011, 09:38 PM   #22
18 guage wire should always be used for low voltage wiring
Mikeym47 is offline   Reply With Quote
Old 12-18-2011, 09:40 PM   #23
Limited Experience
OK. When thermostat is set to call for heat voltage on transformer output is 24.x volts give or take. Honeywell document referenced above says transformer is a 48 volt unit. And when I try and manually engage the system either via the limit switch or by engaging the contactor the voltage drops to 0.
I'm guessing the transformer is bad? And no there were not any transformers in the old stuff not being used.
Does this make sense?
Old 12-18-2011, 09:42 PM   #24
plummen's Avatar
ive never seen a 48v transformer,are you sure its not 48va or something like that?
transformer should read 24-26v as long as there is power to furnace
Old 12-18-2011, 09:48 PM   #25
I'm Your Huckleberry
Rewards Points: 2,270
it is 48 va, not volts.
http://customer.honeywell.com/techli...0s/60-2171.pdf
Thanks.
Doc Holliday is offline   Reply With Quote
Old 12-18-2011, 09:53 PM   #26
A volt-ampere (VA) is the unit used for the apparent power in an electrical circuit, equal to the product of root-mean-square (RMS) voltage and RMS current.[1] In direct current (DC) circuits, this product is equal to the real power (active power) [2] in watts. Volt-amperes are useful only in the context of alternating current (AC) circuits (sinusoidal voltages and currents of the same frequency).
Volt-amps or power demand. Think of it as watts for most purposes.
This device is producing 24 volts (alternating current) and has the ability to provide 50 watts.
Thanks.
Old 12-18-2011, 09:54 PM   #27
how
Rewards Points: 1,104
Assuming the furnace is 30 years+.
Do you have a meter and know how to use it?
There are ways to bypass the upper right hand side and marked (Limit) of the fan/limit control but it is usually 120V and I'm not comfortable explaining it where someone else might get hurt duplicating it. Meter measurement though is possible.
The reason I took Harleys bet is because the older fan/limit controls seldom suffer a failed limit unlike the newer ones. There is a good chance however that you have a secondary limit because your furnace is in a crawlspace and is a horizontal style furnace? Is the furnace's longest side vertical or horizontal?
What you are looking for is another seperate limit control with a reset button on the back of it. It will be between 1 - 3 " across have two wires attached to it.
The fan compartment is the most common location to find it.
Let me know if you find it?
how is offline   Reply With Quote
Old 12-18-2011, 10:02 PM   #28
Jeez man, what did I do to you to insult me like that? Whatever it is, I'm sorry.
Thanks.
Old 12-18-2011, 10:09 PM   #29
how
I will never drink again while posting!
i wiilll never drunk again will pasting.
I will ne're drip again while....
Old 12-18-2011, 10:10 PM   #30
plummen's Avatar
Thermostat issues on old furnace - questions before I replace thermostat. Calab HVAC 11 02-18-2012 08:43 AM
Furnace is in attic, I want to move it because of efficiency issues... SimonSezz HVAC 1 01-22-2011 06:23 PM
tiling under new furnace gramps416 Flooring 4 01-09-2011 10:47 AM
Bryant +80 Gas Furnace won't light tr0910 HVAC 4 01-14-2009 07:11 AM
Tie-in of a Coleman electric furnace nilo HVAC 9 01-03-2007 03:45 PM