Furnace Turns On When It Gets Too Warm - HVAC - DIY Chatroom Home Improvement Forum
Old 06-07-2009, 09:37 PM   #1
Furnace Turns on when it gets too warm
We have to turn the circuit breaker off in the summer because the furnace comes on. Has done this with all three thermostats we have used over the last ten years. AC is separate unit on separate thermostat
wmsward is offline   Reply With Quote
Old 06-07-2009, 11:33 PM   #2
HvacWiz's Avatar
Rewards Points: 252
Is this a electric or gas furnace?
HvacWiz is offline   Reply With Quote
Old 06-08-2009, 07:45 AM   #3
Heater on
Sounds like wrong thermostat or wired for cooling.
SULTINI is offline   Reply With Quote
Old 06-08-2009, 12:40 PM   #4
Agree with Sultini. Sounds like the stat was set to cylce air in fan mode at higher temp and someone has wired it to kick on heat instead.
Chemist1961 is offline   Reply With Quote
Old 06-08-2009, 04:19 PM   #5
DIY'r
ScottR's Avatar
That means it wouldn't work in the winter though..?
I have to ask ...
Does the heat kick on only when you're running the AC?
Or does the heat still kick on even if you set your heating T-stat to 90deg.?
ScottR is offline   Reply With Quote
Old 06-08-2009, 06:56 PM   #6
biggles's Avatar
if the heating stats are all set down to 50F or as low as they can be set you should have no heating during the summer.if the heat starts right off the bat when the cooling starts it is a control mis-wiring.if the heating stats are solid state and set for heat/68F they might be anticipating a call for heat as the cooling drops the temperature within the house
Old 06-08-2009, 11:15 PM   #7
Thanks All;
Furnace is propane. It runs normally during winter. It's on off cycling has no correlation operation of AC which is on separate thermostat and a separate unit.
When it gets up in the eighties in the single wide the furnace will kick on. Not necessarily every time as I have not monitored that yet. There are two wires to the thermostat I think. I have changed it twice from original mercury switch to current programmable thermostat.
I have no recollection of whether this was happening before or started after I replaced motor in furnace six or so years ago.
Old 06-08-2009, 11:22 PM   #8
Heat set in range of 58 to 72 degrees. More likely to come on in high eighties when Air conditioning is off as AC is usually set at about 80 +/- 2*
Lennox Furnace G27M Series Unreliable operation: pressure switch or else? sheppard1977 HVAC 7 01-14-2013 05:42 PM
Carrier Furnace Burner turns on and off continuosly while running Jayenglert HVAC 12 09-28-2011 07:37 PM
Furnace room is warm, wasting heat Richo HVAC 13 02-18-2009 12:57 PM
Problems with new furnace..Overheating, having to reset. Furnace too big? Tommy2 HVAC 41 12-01-2008 01:55 PM
New Cased Coil - Install to Furnace - PICTURES!! hartkem HVAC 39 11-18-2008 01:45 AM