Furnace Supply Temperature Question - HVAC - DIY Chatroom Home Improvement Forum
Old 12-19-2010, 10:18 AM   #1
Furnace supply temperature question
What should the supply temperature be on a 80% 75000 BTU furnace? I've read it should be between 140-160? My registers are getting 120 and my temperature right after the furnace is 148 degrees.
rlukas79 is offline   Reply With Quote
Old 12-19-2010, 10:44 AM   #2
Look inside the furnace for a name plate. There will be a temp rise range given there.
Old 12-19-2010, 11:30 AM   #3
Unless your furnace is cutting out on over temperature safety switch and your filter is not dirty your furnace is running a bit high but with in the acceptable temp rise limits.
On a an 80% I'd like to see closer to a 135*F trunk temp within one to three feet of the plenum but that would be with perfectly designed duct system. And that does not happen.
Why do you ask?
hvaclover is offline   Reply With Quote
Old 12-19-2010, 04:42 PM   #4
That temp is taken right at the bottom of the evaporate coil. When you say temp taken at the plenum to you mean 1-3 feet after the ducting begins? I hav a down draft setup
Old 12-19-2010, 05:52 PM   #5
Ok drilled a hole at about 1 1/2-2f from the beginning of the ducting and got a temperature of 125 degrees