Furnace Sizing - HVAC - DIY Chatroom Home Improvement Forum
Old 09-17-2008, 09:30 AM   #1
Furnace Sizing
Situation:
Heat load caclulation: 59,100 BTU
Proposed Furnace #1 (two contractors):
Efficiency: up to 96.7% @ 60,000 BTU = 58020 BTU (max.)
Two stage / variable blower
Proposed furnace #2 (one contractor)
Efficiency: 95% @ 80,000 BTU = 76000 BTU
How close does the actual output need to be to the calculated Heat Loss? I don't want to be stuck with a furnace running full time on the second stage and yet not being able to keep up with heating the house on cold days.
On the other hand, if the larger furnace is 17,000 BTU higher than the heat load, will it short cycle on those "colder" days?
Swolef is offline   Reply With Quote
Old 09-17-2008, 09:57 PM   #2
I would go with the second furnace despite the fact you think it is oversized. Remember that for the most part, the furnace will be able to heat your house and satisfy your thermostat while running in first stage anyhow.
statman is offline   Reply With Quote
Old 09-18-2008, 11:07 AM   #3
What is the fuel: natural gas or propane?
How was the heat load calc done? If a meticulous job was done with a Manual J then #1 may be okay. If you're not sure then go over the numbers again with whomever did the calc.
Being slightly undersized won't hurt too much, but it hurts when you pay more for a furnace initially and then pay more again due to short cycling. Short cycling may also affect comfort.
Don't forget Manual J is setup to be conservative, so your actual heat loss may lower than that.
dac122 is offline   Reply With Quote
Heil Furnace Burner Problem timothyr HVAC 79 02-12-2014 07:01 PM
Question Re: New Furnace and Duct Sizing DSimo HVAC 3 06-17-2008 07:24 AM
Furnace sizing thumbkins HVAC 5 03-26-2008 08:05 AM
Furnace sizing opinions moneymgmt HVAC 2 05-29-2007 12:26 PM
Replacing My Furnace, few simple questions compression HVAC 10 02-03-2007 05:00 PM