Furnace Runs For A Bit Then No Fire - HVAC - Page 2 - DIY Chatroom Home Improvement Forum
Old 01-29-2013, 07:16 PM   #16
Rewards Points: 150
OK so I got the plug off and checked the pressure was 3.2. I brought it up to 3.5 and of course it does the same thing. It pops the limit switch just before the fan starts, but then after the fan run it will refire and run for 45 min or so and then give the low voltage error code. This time I ran it with the furnace doors open to make sure there was not a air problem. Im at a lost! the only thing I can think of is the board. Any thing else I should try. oh yeah I did check the exhaust and it was 148 just after the fan but went down quick as I checked further up the stack, so it is not blocked
wetbar is offline   Reply With Quote
Old 01-29-2013, 08:58 PM   #17
An old Tradesmen
Rewards Points: 7,414
148 is too high for a condensing furnace. What is the temp rise. 135 is a max, with 120 to 130 preferred.
Sounds like it could be the board bringing the fan on too late. but your flue temp is incorrect for condensing furnace. So check air flow again. Did you look at both sides of the evap coil.
The Following User Says Thank You to beenthere For This Useful Post:
ben's plumbing (01-29-2013)
Old 01-30-2013, 08:20 AM   #18
Rewards Points: 150
according to the owners manual the blower starts 45 sec after the flame is lit, that is about what it is doing. it was 70 coming in and 150 going out.
yes I checked both sides of the coil and even ran it with the doors open. It would still had to go across the coils though.
Old 01-30-2013, 06:59 PM   #19
An old Tradesmen
Almost sounds like a clogged/restricted secondary heat exchanger.
Old 02-01-2013, 10:26 AM   #20
Rewards Points: 150
how do I check inside the exchanger without removing it or buying a expensive camera?
Old 02-01-2013, 03:54 PM   #21
An old Tradesmen
Remove inducer and pull the collector box cover, and look at it.
Old 02-01-2013, 07:00 PM   #22
Rewards Points: 582
tempeture rise according to you is 80 thats to high and if you say blower starts 45sec into heat cycle....why do you think its the board... did you try changing blower speed to see if it changes temp rise...ben sr
Furnace never goes into high fire, why? tfunk HVAC 34 01-23-2013 06:18 PM
Gas Furnace - Only First Two Burners Fire (Video Included) mark2741 HVAC 11 11-20-2012 09:51 PM
What runs before furnace starts rosco HVAC 12 03-20-2010 10:57 AM
my furnace wont fire... please help! chrider88 HVAC 7 01-22-2010 09:43 PM
Problems with new furnace..Overheating, having to reset. Furnace too big? Tommy2 HVAC 41 12-01-2008 01:55 PM