I need to replace my Lennox G26 furnace after blowing thru my second heat exchanger.
Anyone have any favorites? I think important factors to me would be warranty, and heat exchanger design. For example does one brand have a thicker walled exchanger, less prone to cracking, or perhaps one stainless steel that wouldn't rust??
edfiero is offline   Reply With Quote
Old 02-23-2015, 10:19 PM   #2
Rewards Points: 774
Not familiar with that specific furnace, but if you've blown through 2 heat exchangers you might want to look at your ductwork for low airflow or the furnace for excessive sizing.
roughneck is online now   Reply With Quote
Old 02-23-2015, 10:22 PM   #3
Rewards Points: 400
Correct installation can make almost any furnace a great furnace. First thing to make sure of is that the reason for the failure of your first two heat exchangers is corrected, unless it was a design defect of the product itself. I'm not familiar with the G26's.
old_squid is offline   Reply With Quote
Old 02-24-2015, 04:39 AM   #4
An old Tradesmen
Rewards Points: 7,324
Get a properly sized furnace. Yours may be over sized for your home and the duct system.
Old 02-24-2015, 07:01 AM   #5
Rewards Points: 16
House is 2200 sq ft.
Furnace is 75,000 BTU.
I've thought the air flow from the vents was a little weak, but perhaps this is just from using high efficiencey filters. I guess they have to restrict the air flow. Maybe going back to the 2 buck filters would help.
Old 02-24-2015, 08:01 AM   #6
Hvac Pro
Rewards Points: 232
VERY rare to have heat ex failures on them and I see thousands of them and sell Lennox. If it is overheating and cycling on the limit control then any heat ex will fail. The burner gas pressure may be too high along with poor airflow. Need to find out why it is overheating. I would not use any filter higher than Merv 7 or 8 with that furnace. AC coil needs checking for dirt and temp rise thru the furnace also.
There was a factory recall or issue with a few of them where the burner manifold was not welded 100% straight and there was flame impingement on the right burner and it hit the side of the exchanger and caused failures. Lennox had a service bulletin and gave you a new manifold. Dealer needs to check that.
Old 02-24-2015, 09:45 AM   #7
Rewards Points: 312
Installed hundreds of those units back about 20 years ago. Seemed to be a really good model overall. Where do you live?
Just came across a Canadian made gas furnace last spring that uses a stainless primary and secondary on their high end product line. Perhaps other manufacturers out there are doing similar.
Anyone else know of anyone using a stainless primary?
HVACDave is offline   Reply With Quote
Old 02-24-2015, 02:24 PM   #8
Rewards Points: 16
Looks like Thermo Pride and Amana have Stainless Steel heat exchangers. They appear to offer 20 year or Life Time Warrany. Can't beat that.
At this point in my life 20 years and lifetime are probably about the same so I can't loose.
Lennox G40UH furnace stops and fails to start at nights only Muscovite HVAC 20 03-12-2014 01:44 PM
Older Trane 90xl Furnace Perry401 HVAC 1 11-15-2013 12:00 AM
Chimney flue relining or another option - Oil Furnace Expert Needed thp HVAC 22 11-08-2013 09:18 PM
Nordyne furnace, error code: Pressure switch stuck closed. javagrendel HVAC 21 03-25-2013 01:14 PM
Furnace and Water Heater Venting SallySensation HVAC 5 03-05-2013 05:53 PM