Furnace Question - HVAC - DIY Chatroom Home Improvement Forum
Old 03-11-2011, 11:47 AM   #1
mon
furnace question
I have a coleman evcon furnace the blower motor and ignitor comes on, but i have no fire and the code comes up as igniton failure. What could be the problem?
mon is offline   Reply With Quote
Old 03-11-2011, 12:00 PM   #2
rditz's Avatar
do you have the manual?? most manuals will have a troubleshooting section that will recommend corrective action.
if you do not have a manual, contact Coleman, most manufacturers are more than happy to provide manuals for free.
rod
rditz is offline   Reply With Quote
Old 03-11-2011, 03:04 PM   #3
Rewards Points: 5,336
rod
You can probably download one from their website.
Ron
Old 03-12-2011, 11:08 AM   #4
User
If the ignitor energizes then most likely no gas flow. So could be no output from board, low gas pressure, failed gas valve as a few examples. Check to see if there is 24V at the gas valve after the ignitor goes through it's warm up cycle.
Subcooled is offline   Reply With Quote
Old 03-13-2011, 12:08 AM   #5
I agree with Subcooled...you gettin 24v to the gas valve?
What bothers me is....when does the main blower come on (or were you talkin' about the vent motor?)
If the main blower starts before the ignitor works, your faulting out somewhere else sooner, that is, before the gas valve.
Poppyloppy is offline   Reply With Quote
Old 03-13-2011, 07:02 PM   #6
Some furnaces will energize the ignitor but not the valve if there is a pressure switch problem if 90% furnace check drains and venting and just venting on 80% furnaces
heatycooly is offline   Reply With Quote
Furnace supply temperature question rlukas79 HVAC 4 12-19-2010 06:52 PM
Furnace port, and combustion chamber crack question. cjf1980 HVAC 0 07-27-2009 10:23 PM
Gas Furnace Question CoreyK HVAC 8 04-07-2009 06:11 PM
New Cased Coil - Install to Furnace - PICTURES!! hartkem HVAC 39 11-18-2008 02:45 AM