Furnace Question - HVAC - DIY Chatroom Home Improvement Forum
Old 03-11-2011, 10:35 AM   #1
mon
Furnace Question
I have a coleman evcon furnace the blower motor and ignitor comes on, but i have no fire and the code comes up as igniton failure. What could be the problem?
mon is offline   Reply With Quote
Old 03-11-2011, 10:48 AM   #2
Generally,
1. Vent motor comes on
2. sucks pressure switch closed which lets your ignitor work
3. 24v is sent to open gas valve
4. flame uo
5. flame sensor says I've got flame
6. main blower comes on after a timed delay
Note: on any fault, the main blower may turn on
In your case, sounds like your gas valve may not be getting 24v, or may be bad
Poppyloppy is offline   Reply With Quote
Old 03-11-2011, 10:53 AM   #3
mon
Ive measured the voltage, and its getting 24v, Its getting power, but not igniting. I have not located a pressure switch on this furnace, it seems to not have one. I noticed that about after 3 attempts it shuts itself off
Old 03-11-2011, 11:09 AM   #4
Yea, 3 tries and it locks out for a while...you can power off an back on to reset.
If your ignitor is working, it's not your pressure switch. Sounds like a bad gas valve.
Old 03-11-2011, 11:23 AM   #5
mon
The furnace is 14yrs old, so is it possible that the gas valve could be gone bad in that amount of time?
Old 03-11-2011, 11:25 AM   #6
Yes it is. You can pull it off & test it if you have some way to put 24v to it...you'll be able to blow thru it if it's good.
The Following User Says Thank You to Poppyloppy For This Useful Post:
mon (03-11-2011)
Old 03-11-2011, 11:45 AM   #7
mon
Thank you for your help, that was really useful , I will try that.
Old 03-11-2011, 11:48 AM   #8
Welcome, let us know how it goes...we'll all hope it's not the circuit board which is the last thing we would want
Furnace supply temperature question rlukas79 HVAC 4 12-19-2010 05:52 PM
Furnace port, and combustion chamber crack question. cjf1980 HVAC 0 07-27-2009 09:23 PM
Gas Furnace Question CoreyK HVAC 8 04-07-2009 05:11 PM
New Cased Coil - Install to Furnace - PICTURES!! hartkem HVAC 39 11-18-2008 01:45 AM