I'm not looking for code comments, as I know they vary, but just some suggestions.
I have a month-old furnace and during the first firing, the HVAC installer asked for a kill-switch. I put one in while he was at the house, but just used a regular light switch. It is in the attic about 2 feet from the furnace and it protected from physical damage and attached to the truss. It also has the kill switch when the access panel is removed.
Should I install a metal box and switch with a 20amp fuse combo like other furnaces or am I good to go?
Thanks in advance
Sophist is offline   Reply With Quote
Old 12-30-2008, 04:06 PM   #2
An old Tradesmen
Rewards Points: 6,550
No fuse needed or required at the switch, as long as its connected to the proper sized breaker is in the panel box.
Old 12-30-2008, 06:27 PM   #3
Electrician
All appliances require a disconnect, a switch is a means of disconnect.
chris75 is offline   Reply With Quote
Old 12-30-2008, 06:35 PM   #4
Rewards Points: 270
Not sure, might by code need to have the red face plate???
pcampbell is offline   Reply With Quote
Old 12-30-2008, 06:52 PM   #5
biggles's Avatar
that could be considered a service switch which is typical .you might consider cutting one into that attic box and drop another toggle switch into a hall closet or behind a picture with a red painted plate on it.
Old 12-30-2008, 07:00 PM   #6
Electrician
By building code, only oil fired appliances require a disconnect outside of the room of the appliance.
Old 12-30-2008, 10:41 PM   #7
DIY'er
jamiedolan's Avatar
Rewards Points: 1,024
Can a breaker serve as a disconnect if it is a dedicated circuit and the furnace is in the same room as the panel that serves it?
Jamie
Jamie Dolan - Neenah, WI
Jamie Dolan Paw Dogs
Need Help Uploading Photos? Click here.
jamiedolan is offline   Reply With Quote
Old 12-31-2008, 12:38 AM   #8
Jamie
No. Not as sole means of interrupting electrical supply.
Switch is supposed to be readily reachable and in plain site mounted on or adjacent to equipment.
I have a job that has the furnace electrical supply connected to a breaker as you describe. I would not want to have to fumble opening the panel door and then hoping I hit the right breaker in an emergency.
A switch at the equipment takes all the risk out of finding the right disconnect.
hvaclover is offline   Reply With Quote
Old 12-31-2008, 09:51 AM   #9
Electrician
Code reference? Of course a breaker can be used as the disconnect. Check out section 422.31
Old 12-31-2008, 09:52 AM   #10
Electrician
Jamie
Yes a breaker can be used as the disconnect. Check out section 422.31 for all the rules that go with it.
Old 12-31-2008, 09:55 AM   #11
Conflicts with mechanical law. Easier to find one switch on the equipment and not find out that the furnace breaker was mislabeled while turning off at breaker during emergency..
Old 12-31-2008, 09:57 AM   #12
Electrician
Conflicts with mechanical law. Easier to find one switch on the equipment and not find out that the furnace breaker was mislabeled while turning of at breaker during emergency..
What mechanical law are you speaking of? And not saying I would go out of my way to not include a service switch, but just speaking code.
People tend to see something done a certain way for some period of time they tend to believe its actually some kind of law.
Old 12-31-2008, 10:06 AM   #13
Has been included in ever form of mechanical code ever adapted. It is pretty much a unwritten law but more to the fact is it makes sense.
Old 12-31-2008, 10:09 AM   #14
Great Discussion but I failed to convey that the switch I was talking about has a 20 amp fuse with it in the same box. It is metal, has the switch and a small metal cover next to the switch that covers the fuse.
Would this be overkill? New house with 12-2 to the furnace and a 20amp breaker at the sub-panel.
Currently have just a regular light switch next to the furnace.
Old 12-31-2008, 10:25 AM   #15
You are good to go with te existing switch. Can't see why you'd want it fused, though. Breaker should plenty over current protection.
But around here the branch circuits are all protected for 15 amps.
Lennox Furnace G27M Series Unreliable operation: pressure switch or else? sheppard1977 HVAC 7 01-14-2013 06:42 PM
Problems with new furnace..Overheating, having to reset. Furnace too big? Tommy2 HVAC 41 12-01-2008 02:55 PM
New Cased Coil - Install to Furnace - PICTURES!! hartkem HVAC 39 11-18-2008 02:45 AM
Furnace Transfer Switch... caseywa HVAC 16 02-18-2008 10:14 AM
Basic Switch wiring question; Dimmer to Toggle switch (Pictures included) inspectator Electrical 8 08-07-2007 02:19 AM