-   -   Furnace Interlocking for HRV (http://www.diychatroom.com/f17/furnace-interlocking-hrv-136486/)
mk5tdi 03-09-2012 11:51 AM
Furnace: Bryant 340AAV (Gas)
HRV: VanEE 60H (Venmar)
http://www.vanee.ca/literature/install/60H.pdf
I have a questions regarding why alternate interlocking method was used instead of standard for interlocking HRV and Furnace, can someone explain to me how to identify which method is to be used?
Which method to use is based on the type of furnace you have or the type of thermostat mounted on the wall upstairs?
I am trying to understand why its wired the way it is and do I need to change the wiring if I installed a newer thermostat such as the Honewell IAQ with EIM.
According to the HRV installation manual, the "alternate interlocking method" is used and the description of that is following:
"On some older thermostats, energizing the “R” and “G” terminals at the furnace has the effect of energizing “Y” at the thermostat and
thereby turning on the cooling system. If you identify this type of thermostat, you must use the ALTERNATE FURNACE INTERLOCK WIRING."
Here are the pics (on the furnace, the wires on the left go to HRV, the wires that go down they go to the thermostat)
http://img198.imageshack.us/img198/9939/img18411.jpg
http://img849.imageshack.us/img849/8743/img18481.jpg
Here is the wiring as it has been done (Two wires go to furnace and one wire goes to Thermostat):
HRV - Wire - Furnance
NO (Normally Open) - Red - R
C (Common) - Black - G
HRV - Wire - Thermost
NC (Normally Closed) - Green - G
Do not connect G from thermostat to terminal G on furnace
According to the HRV manual the standard way of interlocking would have been as following:
Run no wire from NC on HRV
Connect G from thermostat to terminal G on furnace
HVACDave 03-09-2012 01:08 PM
The alternate method is safest for most installations if you are concerned about feedback through the stat. It appears as though that is done correctly in your case, so all should be good. Are there any reasons as to why you would consider changing it?
mk5tdi 03-09-2012 01:21 PM
Thanks!!!!
The reason why I was considering changing it because when I read the description of alternate interlocking in the HRV installation manual, it seemed to me that it was dependent on the type of thermostat because they said "On some older thermostats..." so I was thinking that if I install a new thermostat then do I need to worry about changing this.
Could you elaborate on what do you mean by "feedback through the stat"?
I am just trying to understand how one method is different than the other and what the NC, C, NO terminals do.
HVACDave 03-09-2012 11:02 PM
The problem with some of the hrv's and stats has been when the hrv doesn't have a set of NO and NC contacts (as yours does) when we energize the G terminal on the furnace control board through a set of dry contacts on the hrv without breaking the G wire that goes to the thermostat then the thermostat doesn't know what to do with a 24 volt input on the G terminal ( as G is designed to be an output terminal from the stat only). The stat would then take the 24 volts coming in on G and activate the A/C, or even the furnace depending on the position of the switching contacts in the stat, and the type of stat used.
We would commonly install an isolation relay to overcome this problem, but the contacts in your hrv do the same thing, so you don't need to do anything else. Hope that answers your question.
mk5tdi 03-10-2012 01:54 AM
Thanks, I am glad I joined this forum, I got two answers to my questions that I have been asking my the company that installed the furnace and HRV for the past week, they never called me back after taking my number.
I just wanted to have an understanding.
mk5tdi 03-10-2012 02:27 AM
Just one last question on this topic to close the loop, today I replaced my thermostat that the builder provided with Honeywell Prestige 2.0 IAQ and the Honeywell Equipment Interface Module (EIM), all seem to be working ok so far (call for heat, HRV turns on just the fan on the furnace and no gas is lit, etc)
I left the interlocking in the alternate position, the way you see in the pics, is that fine?