I have 58MCA060-12 carrier furnace. some time ago, the control board HK42FZ011 was burned out now i replaced it and LED is solid light. I turn on the furnace now. at the thermostat it is showing that it is working but the furnace does not have any ignitor light nor it is working at all
please help me how to troubleshoot
dijas is offline   Reply With Quote
Old 10-27-2012, 02:49 PM   #2
Houston204's Avatar
Rewards Points: 556
Does the induced draft motor even run?
If you get no error codes when a demand is present and it doesn't even try to start, it sounds like the furnace isn't getting 24VAC to the W terminal(s).
Houston204 is offline   Reply With Quote
Old 10-27-2012, 02:54 PM   #3
Thanks for your reply. Nothing is working at furnace
Old 10-27-2012, 03:01 PM   #4
how do i check the voltage to w terminals
Old 10-27-2012, 03:08 PM   #5
how
Rewards Points: 1,104
You could first confirm that the thermostat circuit is not the problem by turning the power off to the furnace. Removing the thermostat wires from their connections R & W on the furnace and then jumping R to W directly with a short piece of wire. Turn furnace power back on to see if the furnace starts up.
Get back to us with the results.
how is offline   Reply With Quote
Old 10-27-2012, 03:15 PM   #6
Houston204's Avatar
Rewards Points: 556
Verify that the wire on the W terminal is not broken... (usually white)
Old 10-27-2012, 03:17 PM   #7
Houston204's Avatar
Rewards Points: 556
How, you are too fast for me
Old 10-27-2012, 03:34 PM   #8
ok I jumped r and w now fan is working and I am getting code 12 thanks
Old 10-27-2012, 03:56 PM   #9
Houston204's Avatar
Rewards Points: 556
12 means power was restored with a heating demand already present.
It lasts about 90 seconds.
Does the induced draft motor, hsi, burners then blower start after the 12 has cleared?
Old 10-27-2012, 04:13 PM   #10
Yes everything is working fine except the wiring to thermo stat. the color of the wire changed some where b/w the furnace . I can resolve that problem by cheking the continuety at furnace and thermostat. I have three set of cable at furnace . One cable has 3 wires green black and white. other cable has black and white and the 3rd cable has only black wire. how these wire shold be connected at furnace and the other end to the thermostat.my thermostat is noma 52-2558-8. you guys are great help. thank you
Furnace Model # Feh-015-04 clicking but not turning on? haimei HVAC 1 12-14-2010 05:01 PM
Payne PG9YAB high efficiency 95% furnace water draining problem jchen64 HVAC 9 12-06-2010 06:42 PM
Carrier Infinity 69 Trouble Code 42 bodya1 HVAC 4 12-05-2010 06:43 PM
Problem with Trane gas furnace quovadis HVAC 17 12-22-2008 01:12 PM
Olsen BFL 120 Furnace DaleB HVAC 12 12-19-2008 10:42 PM