Furnace Cuts Out After A Few Mins - HVAC - DIY Chatroom Home Improvement Forum
Old 12-17-2013, 05:28 PM   #1
Rewards Points: 16
furnace cuts out after a few mins
Hi folks. I searched all I could for an answer before posting this but couldn't find one.
Here is my issue:
The tstat calls for heat and the induction fans starts running, the burner fires and then the blower fan starts, all as per normal.
About 1 or 2 minutes in, the burner goes out and blower fan stops, the induction fan keeps going since the tstat is still calling for heat.
30 seconds or so later the burner fires again and the blower starts again after a short delay. It will do this 2 or 3 times and then run normally after that.
Any ideas? Furnace is a Ruud, I think, have to check for sure.
Tstat is a White Rogers. Filters are new and clean.
Thanks in advance.
chongololo is offline   Reply With Quote
Old 12-17-2013, 05:54 PM   #2
as seen on tv
Rewards Points: 150
sounds like something in the flue pipe possibly. with the given info ,will need to use a meter and see what is opening causing it to recycle. Depending on the year there may be a indicator light you can view there the bottom door that will flash a code
qbert is offline   Reply With Quote
Old 12-17-2013, 06:06 PM   #3
how
Rewards Points: 1,104
A dirty flame sensor in need of cleaning is often the most common cause of this type of momentary flame shut down.
how is offline   Reply With Quote
Old 12-17-2013, 06:47 PM   #4
Rewards Points: 16
Thanks guys, I'll take a look.
Old 12-18-2013, 08:31 AM   #5
Rewards Points: 1,300
Would the blower speed being set too low cause the unit to shut down on overtemp?
danpik is offline   Reply With Quote
Old 12-18-2013, 08:49 AM   #6
Hvac Pro
yuri's Avatar
Rewards Points: 396
It can BUT the fan would keep running after the limit opened, his does not.
Old 12-18-2013, 09:14 AM   #7
Yep, missed that part.
Old 12-18-2013, 06:55 PM   #8
Rewards Points: 16
So I checked the flame sensor and it looked good, I cleaned it anyway.
The LED flashes the code 'pressure switch open'. I took the little air hose off the switch and blew into it and sucked on it and the switch moves just fine.
I let the furnace run and heard some clacking type sounds from these little things in the picture below.
There are two of them wired together about 8 inches apart just above the burners. One wire goes to the board, the other goes to the top part of the combustion chamber perhaps. Are they combustion air sensors?
The hvac guy I called thinks it could be the board though.
Any ideas? Thanks
Old 12-18-2013, 08:20 PM   #9
An old Tradesmen
Rewards Points: 8,234
That is a flame roll out switch. it shouldn't be able to clack.
Old 12-18-2013, 08:40 PM   #10
Rewards Points: 16
ok. What does it do and how does it work? Could that be the culprit?
Old 12-18-2013, 08:47 PM   #11
An old Tradesmen
If there is a problem with the heat exchanger or flue and the flame comes back out toward the manifold, or the shield gets too hot. they open up and cause teh gas valve to close. they are safeties.
Old 12-19-2013, 07:10 PM   #12
Rewards Points: 16
Just a quick update for those interested. I took the vacuum and cleaned out the whole burner area. Those flame roll out switches were sitting on a piece of sheet metal that was sagging a little, leaving them too close to the flame.
I bent the sheet metal up a bit.
The hvac guy came to take a look and thought that the gas pressure was a bit too high and that was also contributing to the over heat cut outs. He turned it down a little.
I put it all back together and so far so good.
Seems to run through a complete cycle just fine.
Thanks to all here for their comments.
Old 12-20-2013, 04:28 AM   #13
An old Tradesmen
Did he adjust the gas pressure by at least using a manometer to see what pressure it was running at before and after the adjustment. or just by eye. If just by eye, he may have covered up the real problem, and it will come back and bite you in the butt some night.
Old 12-20-2013, 03:26 PM   #14
how
Something isn't right here.
Those roll out switches have to be manually re set to allow the gas valve to fire up after they've tripped. If they did cause the gas valve to shut down, one of them is faulty but
your board should also have given you a different fault code.
As Beenthere has indicated, I think you might have just put a band-aide on a real potential bleeder.
Nordyne furnace, error code: Pressure switch stuck closed. javagrendel HVAC 22 04-25-2017 03:02 PM
Furnace and Water Heater Venting SallySensation HVAC 5 03-05-2013 05:53 PM
Moving furnace & redoing ducting cbrc5eric HVAC 0 02-09-2012 08:13 AM
Olsen BFL 120 Furnace DaleB HVAC 12 12-19-2008 10:42 PM
Furnace question cuts off until I hit the reset switch bmvrdv HVAC 7 12-09-2008 09:54 AM