Furnace Cuts Off, Then On, Then Off... - HVAC - Page 2 - DIY Chatroom Home Improvement Forum
Old 09-24-2012, 01:56 PM   #16
how
Rewards Points: 1,070
You seem to be describing a main fan/limit control that is not limiting out. You could replace it but for the info you are giving, your furnace problems could also be from a number of other causes.
If you post actual photos of your furnace then the eagle eyes here might be able to direct you to other possible limiting switches. Have you bypassed your thermostat?
Do you have a meter?
how is online now   Reply With Quote
Old 09-24-2012, 02:02 PM   #17
Rewards Points: 610
http://inspectapedia.com/heat/FanLimitSwitch.htm
the fan control has a hi temp limit function to cut off the burner if heat exchanger over heats..click on attached URL for details.. Read the symptoms/causes and make sure those are addressed first...However, from your description so far, I do think you need a new control.
techpappy is offline   Reply With Quote
Old 09-24-2012, 02:04 PM   #18
biggles's Avatar
push the adjustment pins full CCW but hold that silver dial then reset the fan ON to say 100F and push the hi limit to the stop 200F-220F let the fan come ON see if the burner shuts off right after the fan comes on at 100FNOTE.... what temp the fan does come on off that dial and hovers at.if the burner shuts off right after the fan comes ON...change the control the contacts are aced or the bi-metal pig tail is wornout....measure the pig tail lenght before ordering it...your local Grainger has them
Old 09-24-2012, 05:21 PM   #19
Yes, that is consistent with my observations. I don't think it is the cause of the burner shutdown.
Which brings me here to explore those possibilities.
I will try to post actual pictures. It might take me a few days, though.
No - I have not. Do I do that at the thermostat?
I have a meter and I know how to use it.
Thank you - I hope to have additional information soon.
-dog
landog is offline   Reply With Quote
Old 09-24-2012, 05:57 PM   #20
Rewards Points: 610
starting from your original post all the information points to a defective fan control..IF..you have madse sure there are no air flow problems/blockages e.g., clogged filter, dirty fan, dirty A coil, blocked ductwork..which I presume you have verified as it has been mentioned.
It is not your stat because everything comes on in sequence as it should. It is only after the unit fires up that the burner "shuts off after 2 minutes" That means either there is lack of air flow causing the temperature in the heat exchanger to rise rapidly thereby cutting out the burner..as it is designed to do..then after it cools back down it repeats the cycle again..SO, it is either lack of air flow OR defective control ..nothing else
EXCEPT..maybe blocked venting or chimney? But, in that case there would likely be excess smoke or soot coming from burners and "roll out" of flame...
Old 09-24-2012, 06:00 PM   #21
Rewards Points: 610
you can check the power through the limit switch to see if the switch is opening the circuit it will only do so if temp is exceeded due to previously described possibilities OR if the switch is defective
Old 09-24-2012, 09:38 PM   #22
how
To eliminate the thermostat circuit as the potential problem...
Shut off power to furnace.
Follow thermostat wires where they enter the furnace. They should be connected to a wiring strip with the corresponding letters "R & W".
Disconnect one of those thermostat lines and move it where it can't ground on anything.
Now put a jumper, pigtail or tighten a piece of wire to connect the furnace "R & W" together.
Turn the furnace back on.
The furnace fire should run forever this way.
If it shuts off again like before, your thermostat circuit is not the cause.
Turn off the power and reverse it all the way you found it and its on to the next step.
Old 09-29-2012, 11:10 AM   #23
There is an fan near the top of the furnace that connects to a small duct that leads to the chimney. There is a small tube from this fan that leads to a Tridelta pressure switch model FS 6017-26B. If I disconnect the pressure switch and jump the Normally Open output (after briefly jumping the Normally Closed output) the furnace runs normally.
If I connect a straw to the switch and suck with a meter connected to the switch - it seems to check out okay.
At this point how would I know if the switch should be replaced, or if I should look at whether the exhaust fan is not performing adequately?
I took the switch to my local parts store and they said they didn't have a replacement.
Any ideas?
Thanks,
-dog
Old 09-29-2012, 11:23 AM   #24
AKA HVACTECHFW
Rewards Points: 1,208
call a pro!!!!!!!! In order to properly and safely diagnose your pressure switch problem the furnace needs to checked with a manometer.
IT IS WHAT IT IS
hvactech126 is offline   Reply With Quote
Old 09-29-2012, 02:18 PM   #25
The "pro" that looked at my furnance last year checked it out for about an hour, then told me its operation was normal and charged me for "cleaning."
While I understand your viewpoint, I think I'm much further along toward a solution than the pro.
Thanks,
-dog
Old 09-29-2012, 04:32 PM   #26
AKA HVACTECHFW
Then you obviously didn't hire a "PRO". If you were having this problem while he was in the home checking the unit and he called it normal operation then he was obviously not a pro. You need a manometer and to know how to use it in order to properly check the operation of the pressure switch and then from there determine the correct diagnostic path to follow. A number of things could cause your pressure switch to not operate properly or it may be the pressure switch itself that is bad. You CAN damage a pressure switch diaphragm by blowing or sucking on the tube.
IT IS WHAT IT IS
The Following User Says Thank You to hvactech126 For This Useful Post:
ben's plumbing (09-29-2012)
Old 02-11-2015, 01:26 AM   #27
Rewards Points: 24
i just came across this thread, this is almost exactly what i have. except that I had to retrofitted the board to flame rectification kit to get the led, the original didn't have a led on it. and now when it cuts out several times it locks out. it blinks once per minute. I have a thread on it, i am thinking its the valve or the pressure switch... but no clue. have you ever found your solution?
tlca is offline   Reply With Quote
Tags
amana , ghi90a30 , s8910u
Quote for new furnace. Reasonable? dengle HVAC 16 03-04-2012 08:01 AM
Carrier Infinity 69 Trouble Code 42 bodya1 HVAC 4 12-05-2010 07:43 PM
Problem with Trane gas furnace quovadis HVAC 17 12-22-2008 02:12 PM
Olsen BFL 120 Furnace DaleB HVAC 12 12-19-2008 11:42 PM
Furnace question cuts off until I hit the reset switch bmvrdv HVAC 7 12-09-2008 10:54 AM