Old 10-21-2011, 06:00 PM   #31
Here is a picture of the top of one of the relays where i numbered the connections:
So I tested all of them and got a 1 on my meter for all. But, when testing 3 and 4 together on each of the relays, as soon as I touched them the number jumped up to like 1.50 and then back down to 1.
Again, all 3 had the same results, and it's probably unlikely that all 3 relays are bad.
I'm not sure where to go from here....
spikesnet is offline   Reply With Quote
Old 10-21-2011, 06:50 PM   #32
An old Tradesmen
Rewards Points: 6,156
Should have a marking/diagram of which terminal are the coils, and which are the contacts. Look or it, and ohm out the contacts. Set your ohm meter to 200 or lower if it has a lower setting.
Old 10-21-2011, 07:08 PM   #33
Ok, I think we got something this time. Looking at the relay I numbered, #1 and #2 on all 3 relays is the contacts (blue and black wires).
Relay #3 go negative then positive then settles down around 00.3. The other two relays give a solid "1" on those terminals.
I think I need a relay?
Old 10-21-2011, 07:12 PM   #34
An old Tradesmen
They should be open until they receive 24 volts. The numbers your posting would indicate that they are both closed.
To test your meter. Ohm out the strip heater. should gt 10 to 12 ohms.
Old 10-21-2011, 07:21 PM   #35
Could you please clarify something for me just so I'm not saying the wrong thing....
If I touch my meters two probes together and it displays a "00.2", is that considered open or closed?
Old 10-21-2011, 07:29 PM   #36
ok, I think I figured it out with google, when i touch the probes together I have a closed circuit.
Going to retest.
Old 10-21-2011, 07:35 PM   #37
The strip heater gave me 11.5 - 11.8 on all 3 springs.
relay 1 = open
relay 2 = open
relay 3 = closed
Old 10-21-2011, 08:58 PM   #38
An old Tradesmen
3 is probably the one causing your fan to run.
Old 10-21-2011, 09:23 PM   #39
I'm excited! I think this is it. I just ordered a new relay online, well 5 new relays because that was the cheapest option. I'll update after it comes in and everything is back together.
Thanks for all your help!
Lennox Furnace G27M Series Unreliable operation: pressure switch or else? sheppard1977 HVAC 7 01-14-2013 06:42 PM
My G26 Lennox furnace tries to start for about 5 seconds then shuts down hawkeye2011 HVAC 9 03-26-2011 02:29 AM
Rheem 80% Furnace Short Cycling rlukas79 HVAC 0 12-19-2010 04:27 AM