Furnace Condensation Problem - HVAC - Page 2 - DIY Chatroom Home Improvement Forum
Old 10-15-2012, 04:54 PM   #16
Rewards Points: 610
Did you get the purge times .
It's not what FIELD wants it's what your furnace requires. If it is truly designed for power venting then a draft regulator AND the size of the vent are useless AND maybe detrimental to that application.
BTW when you said it was power vented what exactly do you mean..is the power from the oil burner supply fan or is there a secondary blower or induced draft fan in the FIELD equipment...personally I can't see the purpose of the application..if the furnace incorporates a positive pressure combustion process then all you require is the 4 inch corrugated staimless vent
Also, isn't the existing 4 inch internal for flue gasses and outside diameter 6 inch to allow for combustion air intake OR do I have the sizes wrong?
techpappy is offline   Reply With Quote
Old 10-15-2012, 05:19 PM   #17
An old Tradesmen
Rewards Points: 6,112
Originally Posted by wml52 View Post
Thanks for the info.
BTW, the draft regulator is required as per Field Controls installation and set up manual. One of the things I'm wondering is why they ran 6" pipe when it terminates to 4" at the power vent, why not just run 4" all the way? I would think a smaller pipe 4" would get hotter and stay warmer longer then a 6" pipe? Just wondering...
Bill
Because its suppose to be 6" until the power ventor.
When i the last time it ws cleaned and set up with a combustion analyzer.
Old 10-15-2012, 05:23 PM   #18
An old Tradesmen
It has a fan in the hood of that power ventor. Its a somewhat common set up around here.
Old 10-15-2012, 05:32 PM   #19
Rewards Points: 22
The Field Controls unit is basically a squirrel fan that draws exhaust gases from the burner, the furnace is not a positive pressure combustion chamber. The power vent is used in situations where a normal chimney cannot be used or is not practical, in my case it's a log home with no chimney so the power vent was utilized.
If you look at the photo of the power vent the 6" flue pipe goes into the 4" center of the power vent via a 6' to 4" reducer and the 4" intake duct that exits from the bottom of the power vent is the make up air.
wml52 is offline   Reply With Quote
Old 10-15-2012, 05:36 PM   #20
Rewards Points: 22
The system was looked at by several HVAC contractors that never once looked at the power vent itself. I did however pull the unit and check it over the summer, it was in good condition with very little soot.
Old 10-15-2012, 05:38 PM   #21
Rewards Points: 610
Just looked up the manufacturer's data for your furnace. It is not a positive pressure combustion process as I thought . It is a negative pressure over draft type combustion chamber/natural draft, which would normally vent to a full sized chimney with just a draft control to maintain negative draft over the fire and keep chimney venting properly.
However, what you have is an approved modification to allow direct venting straight outside without a chimney therefore the large discharge flue must be required to meet venting requirements of the furnace.
I think you could mitigate the condensation by closing off the existing combustion air intake (stuff it with non combustible insulation) and provide a separate source for outside combustion air. Check with Field but I don't think that would affect the venting process. It will reduce the cold air surrounding the outlet flue.
Old 10-16-2012, 04:14 AM   #22
An old Tradesmen
Burner has probably been down fired, and the flue is too cold because of that, and probably too much combustion air.
Old 10-16-2012, 09:28 AM   #23
Rewards Points: 610
it's been checked several times by different technicians..doesn't anybody know what they are doing OR..it's just too darn cold in the basement..don't know why it's not being heated but I would heat it. Can't stand cold floors.
Heil Furnace Burner Problem timothyr HVAC 79 02-12-2014 08:01 PM
Help with furnace blower problem Spydey HVAC 6 12-15-2010 09:18 PM
Payne PG9YAB high efficiency 95% furnace water draining problem jchen64 HVAC 9 12-06-2010 07:42 PM
Old Silver-Line furnace problem avro1 HVAC 9 03-18-2010 01:01 AM
Strange Problem with My Furnace chenjijc HVAC 14 11-04-2009 10:05 PM