Furnace Circuit Trips -- Sometimes -- When AC Cycles On - HVAC - Page 2 - DIY Chatroom Home Improvement Forum
Old 08-31-2012, 08:47 AM   #16
retired elect/hvac/plumb
plummen's Avatar
Location: south east of omaha/The island of misfit contractors
Rewards Points: 2,020
Well look at the panel,then look at how many circuits its feeding!
Go kick the electrician in the ass who wired the house with that 20 space panel and have install a 30 space panel atleast to eliminate most of those damn tandem breakers!
"facts" have no relevance to this discusion
Posting from a concrete bunker under a non descript barn
plummen is offline   Reply With Quote
Old 08-31-2012, 11:27 AM   #17
Rewards Points: 1,192
Looking at your breakers,all the twins are wired incorrectly. You electrcian should of seen that and zoomed in on that first.
bobelectric is offline   Reply With Quote
Old 08-31-2012, 12:36 PM   #18
Could you explain how all the tandem breakers are absolutely wired incorrectly?
What I see in the close up photo is that many adjacent tandem breakers are tied across different breaker slots. For example A,B = tandem breaker 1, and C,D = tandem breaker 2; B-C are tied. Since breaker 1 is adjacent to breaker 2, they ought to be on opposite phases. So circuit B and circuit C would be on opposite phases. ASSUMING the electrician wired circuit B and C as a multi-wire branch circuit, or as a single 240v circuit, would this not be acceptable?
sixspeed is offline   Reply With Quote
Old 08-31-2012, 03:26 PM   #19
It appears to me they used a three wire circuit in most of wiring. When you use a twin on leg A, black wire and red wire share the same neutral.You see they add up curent on neutral,so if the blk wire pulls 10 amps and the red oone pulls 14, they add up and overloads the common neutral return. www.mikeholt.com can explain this with graphics.
Old 09-01-2012, 10:04 AM   #20
Rewards Points: 1,520
Also, I guess it might depend on local code but shouldn't MBC breakers be tied together to both trip if one does?
bob22 is offline   Reply With Quote
Old 09-01-2012, 11:10 AM   #21
Rewards Points: 6,652
If you look at the Tandoms, those that are MWBC's have ties on them. Those that are not, don't.
Old 09-01-2012, 11:55 AM   #22
Better eyes than mine!
Lennox Furnace G27M Series Unreliable operation: pressure switch or else? sheppard1977 HVAC 7 01-14-2013 06:42 PM
Dedicated circuit for furnace? DangerMouse Electrical 18 07-03-2010 05:17 PM
New Cased Coil - Install to Furnace - PICTURES!! hartkem HVAC 39 11-18-2008 02:45 AM
Furnace cycles to often DRAZOR HVAC 7 01-03-2008 03:14 PM
Heat Pump compressor trips circuit breaker joejean HVAC 3 08-28-2006 01:15 PM