Furnace Blower Not Working Right. - HVAC - DIY Chatroom Home Improvement Forum
Old 11-10-2008, 04:16 PM   #1
Cool
Furnace blower not working right.
Ive got a 1992 Miller furnace in a mobile home. The heat come on and the blower starts about a minute later and then 1 minute later the blower shuts off but the heat inside the furnace stays on for about 1 minute than shuts off. The blower comes on again without the heat after i turn off the thermostat .The blower comes on for 10 seconds and shuts off again and repeats the same process about 4 times before finally staying off for good.Does anyone have any info that can help resolve this problem? Thanks.
oiljumper is offline   Reply With Quote
Old 11-10-2008, 04:23 PM   #2
Not an HVAC guy. . .if this failure is common for this furnace, the HVAC guys on this forum can nail the cause before I finish typing.
OK
Probably the hi-limit switch shutting it off because there is no cooling airflow, so the hi-limit switch is working normally.
it senses the remaining heat in the system. This is independent of what the 'stat says. The temp.- or time-controlled switch for the blower has recovered and is working normally again, for a while.
when all the heat has finally been dissipated.
The correct sequence for my gas furnace:
the 'stat calls for heat
the inducer motor starts
the gas flame comes on
when the heat exchanger is hot enough the blower starts, either by time passed or by sensing the temp.
when the setpoint is reached the gas shuts off
when the heated air gets cool enough the blower shuts off
some of these depend on time, some on temp. Some are adjustable.
There is also a hi-limit switch which trips if the gas is on but you don't have cooling airflow.
Your problem seems to be in the temp.- or time-controlled switch for the blower motor. It might be set too high, so it shuts off too soon, thinking that the flame is off because the air is too cool. Maybe one of these \/
http://americanhvacparts.com/Merchan...ry_Code=fl-tdf
The second choice would be the control board, but these don't see severe duty like the sensors.
Can you post a furnace schematic?
The good news is I couldn't find any class action lawsuits on the Web against this manufacturer.
Old 11-10-2008, 07:34 PM   #3
HvacWiz's Avatar
Rewards Points: 252
fan/limit switch needs replaced.
HvacWiz is offline   Reply With Quote
Old 11-10-2008, 07:46 PM   #4
Here's another way to look at this.
Let's say the switch costs $50 and a service call costs $300.
50/300 is 1 in 6. If your chances are 1 in 6 or better that the switch will fix the problem, go ahead and replace it.
And the switch is old, anyway.
Just sitting here I'll give you better odds than 1 in 6, but it's not my money riding on this gamble.
Old 11-10-2008, 11:22 PM   #5
An old Tradesmen
Rewards Points: 6,588
Did you just move in to this place.
Or have you lived there, through 1 or more heating seasons before this one.
Some of the operation you describe is usual for that furnace.
Sounds like its getting excessive though.
Bryant 355MAV furnace and A/C blower not starting rajar2 HVAC 39 11-05-2015 02:03 PM
Trane xv80 furnace blower not working jim2138 HVAC 2 03-22-2008 05:55 PM
Blower Not Working sursedur HVAC 2 03-02-2008 09:39 PM
RUUD furnace not working blower runs ddeatrick99@hotmail.com HVAC 2 01-16-2008 10:55 PM
Furnace stops working once a day - help Da_Bears HVAC 2 01-26-2006 02:19 PM