Old 10-30-2009, 10:07 PM   #1
Default Furnace 1st stage won't run
My old 80% Single stage furnace in the attic failed. Had a new American standard 95% TWO stage furnace installed. Runs on Propane. The 1st stage just pops and sputters like a train. The 2nd stage burner runs ok. Installer replaced the whole unit and we still have the same trouble. They even cut the vent stack totally off and no change. After a min on the 1st stage there is water in the vent piping. HVAC guy says it might be a problem with the Propane mixture (too much Hydrogen)??? I have other things on the same propane tank with no problems (older basement furnace, water heater, etc) although they are all single stage units. Are they on the right track??? thanks
ee2009 is offline   Reply With Quote
Old 10-31-2009, 12:01 AM   #2
An old Tradesmen
Ask them if they set up the proper CFM for first stage. Or are they just using factory settings.
If too much air is being moved. It will cause condensate in the primary heat exchanger also. And harm the furnace.
It can cause moisture to build up in the pressure switch hoses also.
You should get moisture in the vent pipe.
Old 10-31-2009, 10:12 AM   #3
Thanks for the reply. Do you mean CFM at the gas port like you would adjust with a jet on a carburator for a car? Sorry, I don't know anything about furnaces. They did have a 2inch intake and exhaust stack hooked up originally and thought that was the problem because the install recommends 3" pipe.
Old 10-31-2009, 11:02 AM   #4
old pro
The unit needs to have the proper venting size, number of elbows/equivalent feet of pipe/slope as per manufacturers specs and all that info is in the install manual.Some furnaces are very specific and finicky about the venting and need to be real close to the manufacturers specs and venting diagram. Did they check the firing rate (manifold gas pressure) on low and high fire?
Old 10-31-2009, 01:04 PM   #5
An old Tradesmen
I was talking about the air blowing through the furnace that goes to the house.
Some furnaces, can move twice as much air as what they should for heating.
Old 10-31-2009, 02:09 PM   #6
Thanks for the reply, I will discuss with the installers...
Old 10-31-2009, 04:40 PM   #7
Question
It is to my understanding that High efficiency furnaces would naturally condensate due to the lack of heat in the venting. That's why they are manufactured with a drain hose inside the unit. Am i missing something here?
thehvacguy is offline   Reply With Quote
Old 11-02-2009, 07:27 AM   #8
thehvacguy: I believe you are correct from what I was told by my installers. The problem they think is the propane mix not being right. Asked me to call Amerigas. Too much (more then would be normal) water condensation for the 1st stage to run correctly. 2nd stage apparently works ok.
Old 11-02-2009, 07:51 AM   #9
An old Tradesmen
Have they ever checked the manifold pressure in first stage.
Have they checked the temp rise in first stage.
Have they checked if its pulling too much combustion air(yes, its possible on a sealed unit).
Have seen the water in the fuel excuse used many times when techs don't know how to check out a furnace properly.
Old 11-02-2009, 11:07 AM   #10
Thanks beenthere: I'm told they checked all that and more. They have an "Expert" coming in from American Standard to check the situation. Not sure when but hopefully this week.
Old 11-02-2009, 11:30 AM   #11
An old Tradesmen
Lets say your furnace is an 80,000 BTU 2 stage.
So in first stage, it would be firing at 52,000 BTUs.
So they are saying that a single stage 50,000 BTU furnace wouldn't work because of the moisture in the LP.
Hopefully the "expert" they're bring. Will really check everything.
Old 11-02-2009, 03:07 PM   #12
I am not sure about your furnace but most furnaces come from the factory set up for natural gas. Most have an LP conversion kit that must be installed before operating the furnace on LP. I believe 2 stage furnaces require different burner orifices and a manifold pressure adjustment. May be other things that need to be set up as well.
SKIP4661 is offline   Reply With Quote
Old 11-02-2009, 06:55 PM   #13
Post up when you get the answer ee. I've seen furnaces not work right if the intallation instructions were not followed but never had water in the propane yet.
Old 11-02-2009, 07:10 PM   #14
Talked to my plumbing company sales rep who talked to the American Standard expert/trainer. Supposedly this is a brand new type of system they are introducing and haven't fully trained all of the installers yet. The 1st and 2nd stages apparently need to be adjusted differently from the normal way of doing gas pressure checks. I was incorrect, this is a three stage system, not two stage.
http://www.americanstandardair.com/H...edom95CRC.aspx
They are coming tomorrow to try again, will let you all know. Thanks for all the support...
Old 11-03-2009, 08:24 AM   #15
on the 3 stage 95 furnace you adjust 1st and 3rd stage and 2nd stage is self adjusting also it is best to use the stainless steel burners with propane so they dont rust
mrairflow is offline   Reply With Quote
More On This Topic
Ice fishing is a popular pastime in the northern states where the lakes and rivers freeze. The ice fishing houses range in sophistication from a little pup tent to a fully built, functioning home. There are several ways to heat the ice fishing house... Read More »
Room additions are an exciting remodeling project. It's nice to anticipate the enjoyment of extra space in your home. But you want the room to be comfortable year round for maximum enjoyment. There are several ways and means to accomplish this. Read More »
So we’re back, and we’re going to show you guys how to get your propane gas grill lit safely and efficiently. We’ve already got our propane tank hooked up, so at this point I’m going to go ahead and show you, this is essentially a... Read More »
Okay, so we have finished cleaning out the hole that we're going to be using and now Rudy and I are going to organize inside of the shanty. Some of the important elements and some of the amenities that might be available to you in a portable shanty are... Read More »
If you're living in a mobile home and facing your first winter, you may not be aware how difficult it can be to keep a mobile home warm. Taking the proper steps to winterize your mobile home cannot only help keep you warm, but keep your heating bills... Read More »
Problems with new furnace..Overheating, having to reset. Furnace too big? Tommy2 HVAC 41 12-01-2008 03:55 PM
New Cased Coil - Install to Furnace - PICTURES!! hartkem HVAC 39 11-18-2008 03:45 AM
Lennox Furnace G27M Series – Unreliable operation: pressure switch or else? sheppard1977 HVAC 5 11-07-2008 06:52 AM
2 Stage AC with older Furnace? SteveTheBuilder HVAC 5 07-18-2008 10:04 PM
condensate removal from my 2 stage gas condensing furnace steamman HVAC 0 01-30-2005 04:03 PM
Copyright ©2000 - 2009, Jelsoft Enterprises Ltd.