#31 |
An old Tradesmen
First time furnace repair. Any advice?
Probably a polarity problem.
Check your wiring, and your grounds. |
#32 |
HVAC / Plumbing
It doesn't sound like ps.. You can jump it out just for testing.. Where did you get the board ?? operation is controlled by the board
#33 |
Polarity shouldn't be an issue. I plugged in everything the same way as it was before.
kenmac >Can you be more specific about "jumping out"? |
#34 |
HVAC / Plumbing
The ps switch will have 2 wires attached. connect them together.. WARNING.... This is a safety & shouldn' t be left jumped out.. Only for testing
#35 |
HVAC / Plumbing
First time furnace repair. Any advice? |
#36 |
An old Tradesmen
#37 |
well, put a new pressure switch just to test it out and that did not resolve the issue. I even took the front fan apart just to check it out. I am really pulling my hair on this.
#38 |
wow, i just noticed 6 blinks. it's not 5 as I initially thought. 6 blinks related to polarity issue. Can someone tell me how do I troubleshoot this issue?
#39 |
An old Tradesmen
I could swear I said a polarity problem earlier.
Recheck your electrical connections. Recheck your ground connections. Has any electrical work been done in the house recetly before your furnace stopped working. |
#40 |
well it's odd. on a video it showed 6 blinks, but i just checked again and it actually blinked 5 times. Nevermind, false alarm about the blinks...
btw, you gave me an idea about connections... technician was unplugging things and plugging them around. Could it be that he plugged in something to the wrong place? Can you tell from the picture if connections are correct? Last edited by klas; 04-13-2009 at 11:34 PM. |
#41 |
Unfortunately, I did not take a picture prior to technician
#42 |
An old Tradesmen
Its acting like a dirty flame sensor, or the pressure switch opening during the burner run time.
A poor ground can cause problems with flame sensing. A loaded ground can cause a false flame sense problem. Check for voltage between neutral and ground. Got some rust in it also. Time to check the heat exchanger for cracks and holes. |
#43 |
I might try replacing flame sensor as well.
#44 |
Try checking if the pressure tap off the inducer is plugged. Could be causing the press switch to fluctuate.
Just slow, not stupid. |
| Display Modes | |
| Help troubleshooting furnace problem | robert_ | HVAC | 21 | 02-15-2012 09:04 AM |
| first time startup on Bryant furnace - furnace calls for heat and will not stop | luvheat | HVAC | 22 | 02-14-2009 09:56 AM |