Old 09-27-2011, 08:09 PM   #1
Fan motor won't turn on; ohms out fine...
So my compressor is kicking on..fan motor does not, so of course the compressor eventually hisses from the internal relief. Ohming out the fan though, I get 30 ohms on C to S, 25 on C to R, & the sum of 55 on R to S..so pretty sure that means the motor's good. What else could be keeping the fan from not turning on? I don't think it could be overpressured, it's been working fine all summer...unless there's a blockage in the lines, which would suck. I left the unit disconnected all night to be sure the fan motor would cool down, & it still won't come on.
reatarted69 is offline   Reply With Quote
Old 09-27-2011, 08:20 PM   #2
Could be the capacitor, or if this is a heat pump, a faulty control board.
Master of Cold is offline   Reply With Quote
Old 09-27-2011, 08:29 PM   #3
I originally thought it was the capacitor as the fan AND compressor wouldn't turn on; it tested bad. So I replaced it, & now the compressor comes on but fan does not..quintuple checked the wiring, too. It is not a heat pump.
Old 09-27-2011, 08:34 PM   #4
Bottom line is if the capacitor is good and there's 240V to the motor and it doesn't run then you buy a new motor.
Old 09-27-2011, 09:51 PM   #5
Mind telling us where the wires from the fan are?
I do the same test on the motors, and have never had a motor test good and not run (unless the bearings are seized).
Old 09-27-2011, 10:24 PM   #6
Alright, I feel dumb..had the C wire from the compressor on the wrong side of the contactor. It's working now..thanks guys.
Old 09-27-2011, 11:33 PM   #7
Its ok..I actually looked at your screen name and figured it out..
Heil Furnace Won't Turn On ada5011 HVAC 1 11-02-2010 08:29 PM
how to make 90 turn of 4" dryer vent in 2x4 wall hohadcr HVAC 5 03-15-2010 10:59 PM
New thermostat-system doesnt turn off RICK430 HVAC 3 12-09-2009 12:40 AM
TRANE XR90 wont turn on newhomeowner08 HVAC 3 12-06-2008 03:59 AM
blower won't turn on in AUTO nhpick02 HVAC 26 12-05-2008 08:27 PM