The second diagram would be on the unit, the first diagram comes in the box with electric heat strips and wouldn't be on your unit if you do not have heat strips. If you have do heat strips, the first diagram probably got tossed by the installer.
If your fan always runs, you may have a faulty stat or a short in the stat wire to your heatpump. If your fan turns off when you remove the G wire, it will verify this.
If the 24VAC signal from your stat to the G terminal isn't the culprit, the fan relay and the heat sequencer controlling your blower should be checked.
If you are TV tech, I'm sure you can test these wires with a meter.
1. Turn off your stat. Verify that the Fan is set to Auto.
2. Measure C to G for 24VAC at your heatpump. It should not be present.
3. Measure for 24VAC at your sequencer coil (5 & 6) and at your fan relay coil (1 and 3). It should not be present with the stat off.
4. Disconnect terminal 4 on your fan relay. If the fan still runs it's your sequencer.
The heat strips would be located at the blower as shown in my first pic. The manual for your unit can be found at the URL displayed near the bottom of my second pic.
Be Careful. Electricity hurts more when you are kneeling in the dirt or mud.