Electric Furnace (only) Blower On Continuously. - HVAC - DIY Chatroom Home Improvement Forum
Old 11-25-2013, 11:43 AM   #1
Rewards Points: 1,586
[QUOTE=justplumducky;1271291]
Originally Posted by justplumducky View Post
I only had a chance to see this furnace for a few seconds, on way out of the home. Going back this morning. I only noticed one sequencer (smaller mobile home) and a fan relay. There was also a contactor relay - was not sticking. T-stat controller was removed from its base.
Relay part number: 9400-13Q152 See pic below.
EDIT: I have both the relay and sequencer on my bench now - no diagram on the relay, but there are 6-ea terminals. 24vac coil. With long side of the rectangular relay positioned vertically in front of me,
#1 & #3 terminals are at bottom (#1 at bottom left).
#2 & #4 terminals are at top (#2 top-left).
#5 & #6 terminals are just below #2 & #4). #5 terminal at left side.
#1 & #3 are the coil terminals, and are good (continuity). With no power to coil, the only other terminals that have continuity are 5 & 6.
With 24vac applied to coil, the only two terminals with continuity are 2 & 4.
I just checked the sequencer with ohm-meter. With no 24v power applied to base, both sets of terminals (base & the only pair on top of that) have continuity across them, but someone just told me this "sequencer" is actually a limit/sequencer. After a second look, I realize now that the bottom of this "seq." looks to be a typical limit switch, with the quarter (25 cents)-sized sensor button on the bottom.
[/B]
Since the only other components in this furnace control box are a contactor relay (not sticking) and the XFMR, one or both of these units (Fan Relay and limit/sequencer) would have to be bad, correct? Changing them both would take care of the problem (FAN on constantly), unless there were a short circuit in the wires to fan motor, Correct? Warm air is also coming out of the registers when fan on.
justplumducky is offline   Reply With Quote
Old 11-25-2013, 04:27 PM   #2
An old Tradesmen
Rewards Points: 6,870
Did you check to see if one of the trip heaters is shorting to ground.
Old 11-25-2013, 04:45 PM   #3
I did not, but will tomorrow.
Googled for "trip heater" and found only the attached Pic, called a Bi-Metal Trip Heater. Is that what you're talking about? Or is trip heater the same as "heating element"? Whichever it is, I'm guessing it would have to be something behind the control panel, where the heating elements are...
I googled some more for trip heater ("images") and all I get is pics of heating elements. You must be talking about one individual element in the set of however many there are in a given electric furnace, yes?
Old 11-25-2013, 05:06 PM   #4
An old Tradesmen
It was a typo. Should have been Strip heater.
The Following User Says Thank You to beenthere For This Useful Post:
justplumducky (11-25-2013)
Old 11-25-2013, 10:21 PM   #5
I did some more googling and determined that my relay is, indeed, working properly, as detailed in my post #1. I ordered a new sequencer/limit switch - pick it up tomorrow, will go install it, and check for grounded heat strip and/or short circuit elsewhere in Blower circuit. Report back tomorrow.
In the mean time, can anyone tell me how this limit/sequencer is supposed to work? Continuity/NC across the bottom set of terminals (for the limit function), and NO (open circuit) across the top set of terminals, for the sequencer function? Cause if that were the case, my limit/seq. is bad then - has continuity across both sets of terminals, with power off.
Old 11-26-2013, 04:51 AM   #6
An old Tradesmen
They may just be a dual element limit. Both closed until trip temp reached.
justplumducky (11-26-2013)
Old 11-30-2013, 01:47 PM   #7
I know I shouldn't admit it, but the problem was a short circuit in the t-stat wires, due to some recent paneling work by the owner's contractor. Another lesson well-learned.
Originally Posted by beenthere: They may just be a dual element limit. Both closed until trip temp reached.
Just thought I would add, at this late date, that you were correct. They both were limits.
Furnace flame and blower alternate 1harleynut HVAC 7 10-29-2013 08:53 PM
blower problems with bryant furnace. blowerissue HVAC 4 03-13-2012 11:34 PM
Quote for new furnace. Reasonable? dengle HVAC 16 03-04-2012 07:01 AM
Payne gas furnace - blower fan running continuously Ed40 HVAC 0 02-05-2011 02:19 PM
Need help with Electric Furnace and HP goodeetwoshews HVAC 7 12-17-2009 09:38 PM