Eco Audit Heat Loss - HVAC - DIY Chatroom Home Improvement Forum
Old 02-23-2012, 07:16 AM   #1
Eco audit heat loss
Anyone know how accurate is the
ECO energy audit heat loss
calculation?
My numbers from ECO are 48676 BTU for heat
and 23878 BTU (2 ton) for cooling.
House is 2000 sq.ft (basement+900sq.ft.)., two
storey, R17 walls and R50 attic, near London ontario
I tried a few on-line heat loss calculations and got
very close 51715 BTU and 52074 BTU.
The original install was 11 years ago they installed
a 70000 BTU furnace and 2.5 ton A/C
Anybody ever have issues with the ECO numbers?
wing 851 is offline   Reply With Quote
Old 02-23-2012, 07:52 AM   #2
if u r asking for just an off the top of the head opinion I would say it's a little light. I live near enough to London to have pretty much the same winter temps.
hvac5646 is offline   Reply With Quote
Old 02-23-2012, 03:53 PM   #3
An old Tradesmen
Rewards Points: 6,846
Could be that in the brand they installed, there is no 60,000 BTU input, so they had to go to a 70,000.
I would think the 2 tons of A/C load is probably fairly accurate. However, would need to know what the sensible and latent gain was, not just the total.
Old 02-26-2012, 09:20 AM   #4
Just did another government calculation and got furnace size of 49000 BTU.
This was using actual gas consumption and degree days. I believe 60000 furnace is best.
I was given quotes on 80000 two stage but makes no sense because will never go to high.
Old 02-26-2012, 11:31 AM   #5
An old Tradesmen
if it only uses degree days, then its not very accurate.
Old 02-26-2012, 12:50 PM   #6
Why do you say it is not accurate?
I said they used gas consumption and degree days for same period.
The calculation was part of CMHC government research study involving 26 houses. The findings were verified using manual j and other software. All 3 methods were consistent with each other. They concluded most furnace installations are grossly oversized.
Old 02-26-2012, 01:04 PM   #7
An old Tradesmen
Degree days doesn't account for night time conditions.
At 20 degrees outdoor temp at 2:00PM, a home needs less heat then at 2:00AM at 20 degrees outdoor temp.
Degree days is an average, so its not accurate for determining heat loos, or gain.
Old 02-26-2012, 10:04 PM   #8
Using HVAC-Calc I got the following:
Sensible Gain = 17688
Latent Gain = 2220
Heat Gain = 19908 BTUH
Heat Loss 43778 BTUH
I will be replacing it with 60K furnace and 2 Ton A/C unit.
A question about heat loss rate deerhunter HVAC 5 11-19-2010 04:40 PM
Upgraded to new Hunter model 44860 thermostat and now no emergency heat hlmaint HVAC 0 01-08-2010 01:17 PM
Heat Loss Related Question mynd66 HVAC 14 10-25-2009 02:42 PM
Hi new here- heat loss help. newbieowner Green Home Improvement 11 02-13-2009 02:24 AM
Heat Loss Gain how to calculate jufix HVAC 1 11-20-2007 02:46 PM