Old 11-13-2009, 12:54 PM   #1
Duo Therm Oil Furnace problem
I have a Duo Therm oil fired furnace which I have changed the pump and nozzle. It fires up and run great foe 24-36hrs then shuts down. When it starts up after resetting it rumbles. The electrodes are rounded at the tips and approx 3/16" apart. Any sugestions on what to do next.
processtech is offline   Reply With Quote
Old 11-13-2009, 01:06 PM   #2
Hvac Pro
yuri's Avatar
Rewards Points: 2,238
Hate to say it but you would be better off to get a Pro to check it and set it up properly with a combustion analyzer. When it rumbles that can be dangerous as you may be getting delayed ignition or have an excess of unburnt oil in the chamber from a bad spray pattern and that is dangerous. Not something we can talk you thru on the net.
Old 11-13-2009, 01:21 PM   #3
It rumbles and then starts up, it does not shut down on start up.
Old 11-13-2009, 02:45 PM   #4
An old Tradesmen
Rewards Points: 7,304
Rumble=uncontrolled fire.
Old 11-13-2009, 02:56 PM   #5
Could it be that the electrodes are worn down as they have rounded tips. I was told they should be pointy and 1/8" apart. Could that make an intermitend problem?
Old 11-13-2009, 03:30 PM   #6
An old Tradesmen
Along with many other things.
After you changed your nozzle and pump.
What was your CO2 reading, and what was the draft over the fire.
Too low on one will cause this also. And too high on the other does also.
Heil Furnace Burner Problem timothyr HVAC 79 02-12-2014 07:01 PM
Strange Problem with My Furnace chenjijc HVAC 14 11-04-2009 09:05 PM
Help - Problem with Oil Fired Forced Air Furnace JohnF HVAC 13 01-31-2009 09:04 PM
Carrier Furnace Problem Boats1183 HVAC 1 11-11-2008 06:41 PM
another question for a miller furnace problem jb9270 HVAC 1 02-05-2007 02:04 PM