Dunkirk Xeb5 Boiler Problem - HVAC - DIY Chatroom Home Improvement Forum
Old 09-08-2012, 11:04 PM   #1
Dunkirk xeb5 boiler problem
I bought a XEB5 dunkirk boiler 2008 model and we got it hooked up and it melted the inducer motor in about 3 min. of running.Any ideas what the problem could be?
Thanks for any help.
Kurt
benznut is offline   Reply With Quote
Old 09-09-2012, 07:27 AM   #2
An old Tradesmen
Rewards Points: 6,140
Are you on natural gas or LP.
Old 09-09-2012, 08:44 AM   #3
I'm on natrual gas.
Old 09-09-2012, 08:50 AM   #4
An old Tradesmen
Any chance it came through set up for LP?
What was the manifold pressure.
Old 09-09-2012, 06:41 PM   #5
It was set up for lp and we changed the orffices over to natural gas.We never got a chance to check the manifold pressure before it melted the blower so i'm not sure what pressure thats at.
Old 09-09-2012, 07:03 PM   #6
An old Tradesmen
If it was set up for LP. Then the manifold would have been set to at least 10", where as nat gas is only 3.54".
You'll need to get the nat gas spring, and set it to 3.5". And of course a new inducer.
Old 09-09-2012, 07:35 PM   #7
Ok i'll get a new inducer and see if we can't get it to run long enough to check pressures.
Kurt
Old 09-09-2012, 07:36 PM   #8
An old Tradesmen
Don't forget. You must get the nat gas pressure spring in order to use it on nat gas.
The Following User Says Thank You to beenthere For This Useful Post:
hvactech126 (09-09-2012)
Old 09-24-2012, 08:44 PM   #9
dunkirk problem continues
I got a new inducer and set the manifold pressure at 2.5 and melted another inducer.Any more ideas.
Thanks Kurt
Old 09-24-2012, 09:29 PM   #10
An old Tradesmen
Are you sue you have the right size nat gas orifices in it.
Must be a roaring flame. or else no water in the boiler.
Old 09-24-2012, 09:52 PM   #11
The flame looked good.I don't why they would put the plactic inducer on it.
Old 09-24-2012, 10:10 PM   #12
An old Tradesmen
Is this the blower part number you have, Substitution: 2272156
Old 09-25-2012, 07:21 AM   #13
Yes that is the part number.
Old 09-25-2012, 11:56 AM   #14
An old Tradesmen
Make sure if that boiler is suppose to have baffles in the flue ways, that they re there.
Burnham boiler banging/thumping noises quadradeuce HVAC 6 10-02-2010 10:55 PM
Hydro-Shark Boiler problem sack Plumbing 4 01-12-2010 03:29 PM
Problem with Utica boiler starting billygeg HVAC 3 01-04-2010 09:07 PM
Radiator Boiler Problem JmalikS Plumbing 3 01-12-2009 11:09 AM
Utica Boiler shut down problem halo HVAC 2 02-29-2008 08:41 PM