Old 10-29-2011, 10:23 PM   #16
Read this, start with section 28.5.1 this will get you ballpark numbers very quickly
http://www.alpinehomeair.com/related/Ductwork.pdf
The manual X,Y,Z books give you over precisely incorrect results to the 12th decimal place. (Because there are so many inputs to the equation, most of which are approximates or unknown.)
The supply side needs more attention then the return, the return can never be too big, but should at least be bigger then the supply side (carry more cfm). The supply size can be too big or too little, but it's better to be too big.
Figure out what each room needs according to the tables in ductwork.pdf, then work backwards, make sure each trunk line is big enough to supply all the branches off it. It helps to reduce the trunk size just after a branch is taken, this will keep the pressure constant for the next branch down the line.
The branches/takeoffs/elbows are where all the resistance is, make them as smooth as possible, read this
http://www.perfect-home-hvac-design....-fittings.html
if you are forced to use a bad branch or multiple wacky elbows, make the duct one or two sizes larger then the calculations show, this will reduce the resistance.
Plenum takeoffs should be at least 30 inches from the bottom of the plenum, but at least 6 inches below the top of the plenum.
Most people make the ductwork too small, mainly to save space.
Good luck!!!!
bungalow_steve is offline   Reply With Quote
Old 10-29-2011, 10:45 PM   #17
An old Tradesmen
Rewards Points: 8,154
That PDF under sizes all the duct work.
Old 10-31-2011, 08:23 AM   #18
Maybe for a hack job (bullhead tees, no turning vanes, long branches >25 feet, flex duct) but for a pro job with low TEL they are industry standard proven. As I said in my post, increase the size by one or two if you can't do it right.
Old 10-31-2011, 04:13 PM   #19
An old Tradesmen
They are industry short cut standard, not proper.
I've measured the static on many of those "short" run jobs. And they are always higher then .5" TESP. And thats sheet metal and hard pipe jobs.
The average supply run is more then 40' of TEL. And thats not including a PD for the register, or a balancing damper.
Adding new ductwork to a second floor. vr4Legacy HVAC 4 01-27-2011 10:51 AM
Ductwork Insulation tk3000 HVAC 3 11-19-2010 04:08 PM
Sizing and installing Ductwork. 50juan HVAC 30 07-09-2010 09:25 PM
plastic ductwork vs. metal: acoustic duct liners jjpclev HVAC 5 02-26-2010 07:29 PM
Moving ductwork to accomodate finished basement Badfish740 HVAC 1 01-13-2010 03:11 PM