Ductwork Sizing Help - HVAC - DIY Chatroom Home Improvement Forum
Old 10-29-2011, 01:40 AM   #1
Ductwork sizing help
Hi, I sure could use a hand getting my ductwork properly sized. My home had a floor furnace with no ductwork that I removed. I bought the HVAC -CALC program to do a manual j on my house . That worked great. I bought the manual d book but just can't puzzle it all out. I have all the numbers from the manual j and really need help figuring out the size for the duct. I have a diagram of how I think it should be layed out just no sizes . Can any one help or point me to the right place? Thanks in advance, Tyler
tylerhudson01 is offline   Reply With Quote
Old 10-29-2011, 04:47 AM   #2
An old Tradesmen
Rewards Points: 6,904
Post diagram, and all lengths of ducts.
Old 10-29-2011, 11:08 AM   #3
first floor
Old 10-29-2011, 11:18 AM   #4
The second floor. The supply from the first floor is 10'. I have the specs for my blower motor for the furnace but am unsure at what speed it will operate.
Old 10-29-2011, 11:19 AM   #5
This is the second story.
Old 10-29-2011, 02:29 PM   #6
An old Tradesmen
You have roughly 120' of TEL for the longest supply. I don't see any return duct work drawn.
Old 10-29-2011, 03:18 PM   #7
It is in the first scan. It will be appx. a 5' run. Just beside the furnace.
Old 10-29-2011, 03:20 PM   #8
An old Tradesmen
Does it go straight up to a floor register?
Old 10-29-2011, 04:04 PM   #9
Yes. I would like to use round duct through out the system except the return.
Any thing else you need , just ask as I am unsure as to what to post for you. Tyler
Old 10-29-2011, 04:19 PM   #10
An old Tradesmen
The return will add another 105 foot of TEL. So you have roughly a total of 225 foot.
Add up at the other pressure drops, air filter, supply boot(just one), return grille, dampers, A/C coil. Subtract this from the furnaces rated ESP, most likely .5". this will give you the ASP(Available Static pressure). Say it comes out to .22" ASP.
>.22/225=.000927, .000927X100=.097. So you would use .09" friction rate in that example.
Old 10-29-2011, 04:32 PM   #11
So how can I determine the duct size to each vent? When I did the manual j it gave me the cooling and heating cfm for each room at a given amount of cfm from the equipment. If I post that would that help?
Old 10-29-2011, 04:35 PM   #12
An old Tradesmen
Need a friction rate slide chart, or use the charts in manual D.
Use the info I posted above to determine the ASP you have and the friction rate to use. then select the duct size that will carry that CFM to the room.
Old 10-29-2011, 05:12 PM   #13
I appreciate the help but I guess I am just not getting it. The math is overwhelming and honestly I am unable to perform it. I guess I will have to figure out a different way.
Old 10-29-2011, 07:11 PM   #14
An old Tradesmen
Look at how many CFM a room needs, then look in the manual D book at the amount of air a X size pipe will flow at say .07" friction rate, that is the size pipe you use.
EG: A room needs 80 CFM, using .07" FR, a 6" round will fl;ow that amount.
Old 10-29-2011, 09:47 PM   #15
That makes a little more sense , I'll give that a try. Thanks , Tyler
Adding new ductwork to a second floor. vr4Legacy HVAC 4 01-27-2011 10:51 AM
Ductwork Insulation tk3000 HVAC 3 11-19-2010 04:08 PM
Sizing and installing Ductwork. 50juan HVAC 30 07-09-2010 09:25 PM
plastic ductwork vs. metal: acoustic duct liners jjpclev HVAC 5 02-26-2010 07:29 PM
Moving ductwork to accomodate finished basement Badfish740 HVAC 1 01-13-2010 03:11 PM