Duct (argh!)... - HVAC - DIY Chatroom Home Improvement Forum
Old 02-01-2012, 09:01 AM   #1
MarginallyQualified
Rewards Points: 2,464
Duct (argh!)...
Total Duct Trunk run is 36 feet feeding a total of 9ea branch ducts.
These are all 6 inch round and about 10 feet long the register boot.
Five of these tap off the side of the trunk, then under a beam and up.
Three go all the way to the wall; two stop short (bathrooms).
Four of these ducts tap off the top of the trunk; go all the way to the wall.
Assuming that these 9 branch ducts and registers work and are staying put...
what size(s) of duct **should** the trunk they are attached to be?
Thanks.
Here's the (rough) Trunk & Branch layout:
_|___________________|______|___________________|_ _______|__
-----|-------|--<80K>----------------------------------------|---------------|-
|<--3'->|<----8'---->|<-----6'------>|<-----9'----->|<-----10'---------->|
Old 02-01-2012, 09:53 AM   #2
need to know what size furnace, house size, how many tons of air .
model of furnace would help too.
hvac5646 is offline   Reply With Quote
Old 02-01-2012, 04:46 PM   #3
MarginallyQualified
Originally Posted by hvac5646 View Post
need to know what size furnace ...lets say 70-80,000 Btu; 90%+
house size ...lets say 1300SF; single floor R32 ceiling etc
how many tons of air ...lets say 24,000 Btu or 2T
model of furnace would help too ...yet to be determined
Feel free to plug in (assume typical?) for anything else that you might need (CFM; SP, etc)
Old 02-01-2012, 05:16 PM   #4
An old Tradesmen
Rewards Points: 8,168
1300 sq ft in NC only needs a 70,000 BTU 90% plus furnace if its made of all glass.
Old 02-01-2012, 05:47 PM   #5
MarginallyQualified
If you say so..
The question is about sizing duct.
Old 02-01-2012, 05:50 PM   #6
GC/Master Plumber/Mech
Rewards Points: 560
Tarhell, PM me your email and I wil send you a deal about duct work that may help you.
John Wayne once said "Life is tough and it is even tougher if you are stupid"
Tempstar and Trane Dealer
Old 02-01-2012, 06:01 PM   #7
REP
If the furnace and coil is at one end ,20x8 would do it.If the furnace is somewhere in the middle that would change.
What is all that 3',8',6',9',10' all about?
Now while I have seen a few supply side mistakes,Return air ducting mistakes are way more common.
On 2 ton you would like to see at least a 24x8 drop.
REP is offline   Reply With Quote
Old 02-01-2012, 06:06 PM   #8
MarginallyQualified
These are the distances between the various areas where the trunk gets tapped.
I'm assuming that the whole trunk shouldn't be done with one size.
Do you get how the | indicates those 6" branch ducts?
The (rough) Trunk & Branch layout:
_|___________________|______|___________________|_ ________|__
-----|-------|--<80K>----------------------------------------|-----------------|-
|<--3'->|<----8'---->|<-----6'------>|<-----9'----->|<----7'---->|<---3'-->|
If the furnace and coil is at one end...
It's not. See that 80K at about 1/4 way into the run?
One bridge at a time. Thanks
Old 02-01-2012, 06:07 PM   #9
An old Tradesmen
Originally Posted by TarheelTerp View Post
If you say so..
The duct work is sized to the mode that requires the most air flow. A 70,000 BTU input 95% efficient furnace requires a lot more air flow then a 40,000 BTU 95% efficient furnace. 1000CFM for the 70, and 600 CFM for the 40.
So how can you size the duct work, without knowing the air flow you need.
Old 02-01-2012, 06:18 PM   #10
OP PMed me with this:
Ever install any Kelvinator stuff?
I'll probably end up with Lennox or Rheem...
but it would be great to have a benchmark to see how much the name brand premium comes out to.
Would you mind checking your wholesaler?
Kelvinator Furnace KG7SC-072D-024; 66,000Btu; 95% (25B141)
you are not allowed to solicit contractors by PM.
And since when is it customary to ask a contractor what his costs on equipment are?
Old 02-01-2012, 06:32 PM   #11
MarginallyQualified
You drop back ten and punt.
Isn't it your practice to install all new duct on every replacement job?
The Q: Assuming that these 9 branch ducts and registers work and are staying put... what size(s) of trunk duct **should** they be attached to? Thanks.
Old 02-01-2012, 06:41 PM   #12
Rewards Points: 560
Tarheel, send me your email address and I can send you a booklet helping you understand alittle better of how to size duct. PM it to me
Old 02-01-2012, 06:59 PM   #13
An old Tradesmen
Is that 9-6" branches each carrying 70 CFM, 100 CFM, or do some of them carry less then others.
On replacements, I test the duct to see what it can carry, and put in the right size equipment for the house. not just some arbitrary size.
Now is the time to do the load calc, and get the right size equipment. Instead of just guessing at a size, and not having a good system.
The Following 2 Users Say Thank You to beenthere For This Useful Post:
ben's plumbing (02-01-2012), Plumber101 (02-01-2012)
Old 02-01-2012, 08:16 PM   #14
MarginallyQualified
I agree entirely. And I would even pay good money to have someone produce those numbers for me. But so far, and even with asking for it specifically...
the people from the top companies I've had in aren't doing this.
It's all "don't look for the man behind the curtain" and "this should be OK".
But that is still a whole other set of discussions.
Back to THIS discussion (if you're inclined to do so)... The Q remains:
Assuming that these 9 branch ducts and registers work (they do fine)
and are staying put (they are)...
Feel free to plug in (assume? typical?) for anything else that you might need
(CFM; SP, blower speed, etc) or commonly find/input. Thanks
Old 02-01-2012, 08:19 PM   #15
An old Tradesmen
HVAC CALC.
Do your own load calc.
?an Insulated Flexible Duct - half attached and half unattached ? tran Roofing/Siding 2 06-21-2012 06:25 PM
My Duct Sealing Project Cakemeister HVAC 6 06-13-2011 11:45 AM
Planning on New duct work..any feedback... kilosos2 HVAC 28 01-26-2011 09:21 AM
Metal duct or flex? smokey982 HVAC 6 08-06-2010 06:20 AM
Condensation in Wall: Can I Seal a Dryer Duct With Caulk? xquercus HVAC 5 07-01-2007 02:33 PM