Dual capacitor mfd
What would happen if you install a 35-5 mfd capacitor and the unit requires a 40-5 mfd ? Or visa versa?
lsmartin is offline   Reply With Quote
Old 07-11-2012, 06:18 PM   #2
The rule is is you have to stay within 10% of the original rating you'll be ok....however, I see 5 over or under the rating of the original cap being used all the time.
Best bet is use what the original spec called for.
hvac5646 is offline   Reply With Quote
The Following User Says Thank You to hvac5646 For This Useful Post:
ben's plumbing (07-12-2012)
Old 07-12-2012, 10:04 AM   #3
Either won't start or burn the unit.
clocert is offline   Reply With Quote
Old 07-12-2012, 06:49 PM   #4
that is incorrect.
Old 07-12-2012, 08:19 PM   #5
Originally Posted by hvac5646 View Post
that is incorrect.
Shorten the motor life?
The Following User Says Thank You to Yoyizit For This Useful Post:
plummen (07-14-2012)
Old 07-12-2012, 10:32 PM   #6
I've seen several where the compressor label says 45mfd and the unit mfr. uses a 40mfd. They said testing showed a better SEER with the capacitor they used instead of the one on the compressor tag. As HVAC said use what's specified by the mfr.
Old 07-12-2012, 11:49 PM   #7
If call for 40uf, you install one with only 20uf, it won't start.
Old 07-13-2012, 12:34 AM   #8
the op asked about going 5mfd over or under...not dropping from a 40mfd to a 20.
ben's plumbing (07-13-2012)
Old 07-13-2012, 04:51 PM   #9
I could swear I've seen start run electrolytic capacitors with a -10%, +50% tolerance but I can't find them now.
Here's what I found with
http://www.google.com/search?client=...UTF-8&oe=UTF-8
+/-6%, 2 ea. cases
+/-5%, 3 ea. cases
270-324 MFD (~+/-10%), 1 case, Grainger
161-193 MFD (~+/-9%), 1 case, Grainger
and
"a start capacitor rated 10% over or 10% under the recommended MFD rating can be substituted"
"A 20 % tolerance is acceptable for start capacitor values less than 200 MFD."
In general, the farther you are from design center values the more likely you can expect problems. How relevant capacitor sizing is in light of all the ways motors can be abused is hard for me to say.
One link had you trying +100% and -50% capacitor values so we don't seem to need, nor can we get, nor is it financially feasible, to get +/-1% on these units.
Old 07-13-2012, 05:10 PM   #10
JJboy's Avatar
(2652 x Amps) / Volts
Amps- at S Terminal
Volts - at Herm and C
Check if it will be close to 40MFD
**Always kill the power ** Hot air rises, but heat will always move from higher to lower temperatures. ** Real man shoot in manual. ** If it ain't grounded, it ain't dead.
JJboy is offline   Reply With Quote
Old 07-13-2012, 08:31 PM   #11
Actually, it's 2653. 1,000,000 x 1/(2 x PI x 60), for 60 Hz.
Old 07-13-2012, 11:04 PM   #12
My units take a 35/5 cap. Before the #1 unit cap was replaced it was testing right around 30, so 5 under. I didn't notice anything wrong with the unit (started and ran fine). However long term I would suspect you would damage the compressor.
wheelsup is offline   Reply With Quote
Dual Stage Furnace grod777 HVAC 34 11-05-2011 11:28 AM
NM cable and Dual fuel range edge130 Electrical 0 11-02-2011 04:48 PM
Dual Cap 35/25MDF 440VAC JJboy HVAC 20 10-10-2011 10:12 PM
Dual Pane Windows No Low E Glass and No Argon Gas Filling AZSun Windows and Doors 4 08-12-2011 10:10 PM