Does The RES Spec On The Side Of Contactor Refer To Resistive Amps? - HVAC - DIY Chatroom Home Improvement Forum
Old 06-29-2014, 08:59 PM   #1
Rewards Points: 1,472
Does The RES Spec On The Side of Contactor refer to Resistive Amps?
Looking at a new contactor - single pole, 24v coil
VAC...........FLA....LRA......RES
240/277....30.....180......40
Can I assume the "40" is a resistive amps number and A/C fan, blower and compressor motors are not resistive loads?
justplumducky is offline   Reply With Quote
Old 06-30-2014, 01:29 AM   #2
I'm Your Huckleberry
Rewards Points: 2,270
Volt-ampere (VA) is a measurement of power in a direct current ( DC ) electrical circuit. The VA specification is also used in alternating current ( AC ) circuits, but it is less precise in this application, because it represents apparent power , which often differs from true power .
In a DC circuit, 1 VA is the equivalent of one watt (1 W). The power, P (in watts) in a DC circuit is equal to the product of the voltage V (in volt s) and the current I (in ampere s):
P = VI
In an AC circuit, power and VA mean the same thing only when there is no reactance . Reactance is introduced when a circuit contains an inductor or capacitor . Because most AC circuits contain reactance, the VA figure is greater than the actual dissipated or delivered power in watts. This can cause confusion in specifications for power supplies. For example, a supply might be rated at 600 VA. This does not mean it can deliver 600 watts, unless the equipment is reactance-free. In real life, the true wattage rating of a power supply is 1/2 to 2/3 of the VA rating.
When purchasing a power source such as an uninterruptible power supply ( UPS ) for use with electronic equipment (including computers, monitors, and other peripherals), be sure the VA specifications for the equipment are used when determining the minimum ratings for the power supply. The VA figure is nominally 1.67 times (167 percent of) the power consumption in watts. Alternatively, you can multiply the VA rating of the power supply by 0.6 (60 percent) to get a good idea of its power-delivering capability in watts.
Thanks.
Doc Holliday is offline   Reply With Quote
Old 06-30-2014, 07:03 AM   #3
P = VI
Thx Doc. I had google and found that online also, because I was wanting to know how to calculate the current a xfmr puts out (found: VA divided by Volts). I found that same article, but don't see how it applies to my contactor question.
Old 06-30-2014, 09:42 AM   #4
Rewards Points: 380
I believe the RES is the Resistive amps that the contacts are rated to handle the current load of. Some will give hp ratings at different voltages, and FLA as you described, But the RES is a higher value primarily because there is no inrush current to be worried about in a resistive load. At least that is my understanding. Perhaps a site like FURNAS may have more information.
HVACDave is offline   Reply With Quote
Old 06-30-2014, 10:54 AM   #5
Hvac Pro
yuri's Avatar
Rewards Points: 1,122
It is resistive load. Contactors are used to turn on elements in some electric furnaces and that is a pure resistive load.
Old 06-30-2014, 05:35 PM   #6
So the "40" number for a resistive load, which I assume means a relatively constant load (heat strips on an electric furnace), as opposed to a variable speed (variable load) PSC Motor, means 40 Amps?
Thanks HVACDave, I'll check out that site.
Old 06-30-2014, 06:01 PM   #7
JOATMON
ddawg16's Avatar
Rewards Points: 818
Most contactors can handle a higher resitive vs inductive load.
Old 06-30-2014, 08:47 PM   #8
An old Tradesmen
Rewards Points: 6,112
Yes, resistive is strip heaters. Motors are inductive loads.
Timing for rebuilding of side entry: Help! navi_jen Remodeling 0 06-16-2010 11:02 AM
Should I use a vapor barrier on each side? Hossenfeffer Building & Construction 3 04-09-2010 11:12 PM
Brain Lock, help a guy out Bigfoot Electrical 13 06-02-2009 09:08 AM
Question about sharing nuetral (as in 12/3) wire Piedmont Electrical 19 01-22-2008 09:39 PM
Side By side refrigerator Susie Q Appliances 6 08-31-2007 04:26 PM