B vents less than 12” in diameter, terminate 2’ above any vertical surfaces within 8’. (G2427.6.5 #1)
B vents with vent caps 12” in size or smaller shall terminate a minimum of 12” from roofs when 6/12 or
flatter. See Tbl. 8-A for other. (G2427.6.5)
Vent clearances to combustibles per manufacturer’s listing or performance standards. (M1803.3.4,
M1306.2, G2427.7.7)
Single wall vents cannot penetrate a wall, floor or ceiling
without a listed pass through assembly.
(M1803.3.1, G2427.7.4)
Vent terminations installed per the manufacturer’s listing. (M1804.2.1)
Venting systems terminate not less than 4’ below or 4’ horizontally from, and not less than 1’ above a door,
an
operable window or a gravity
air inlet into a building, nor less than 3’ above any
forced air intake within
10’, nor
within 12” of grade. (M1804.2.6 & G2427.8 )
Vent terminal not mounted directly above or within 3’ horizontally of a gas meter or oil tank. (M1804.2.6)
Vent terminal no closer than 3’ to an interior corner formed by (2) perpendicular walls. (M1804.2.6)
Power exhaust terminals not located within 10’ of property line and adjacent buildings. (M1804.2.6)
Where vents extending into an attic pass through insulated assemblies, an insulation shield of 26 gage
sleeve not less than 2 inches above the insulation, secured in place and maintain required clearances to
combustibles. (G2426.4)
Venting supported per manufacturer’s listing. (M1803.3 & G2427.5.7)
Vent connector joints are fastened with sheet metal screws or rivets. (M1803.3)
Vent and chimney connectors installed within the same space that the appliance is located. (M1803.3)
http://www.mybuildingpermit.com/Insp...0checklist.pdf
Check with local B.D. before you close off part of a window or run it outside to " bend up 90 degrees to above the roof ".
Be safe, Gary