Disabling LO setting on boiler
I have an oil boiler with a Honeywell L7224 aquastat. There's a DHW coil installed but I no longer wish to use it, since it was burning up a lot of oil outside of heating season. A 40 gallon electric water heater was installed off of the coil.
Question is, I want to disable the LO setting on the boiler, that existed for the DHW coil. I downloaded the manual, and managed to drop the low down to 110 degrees (as low as it'll go). The only settings I can change are HI, LO, DIFF, and F/C temperature display. I contacted Honeywell and they refuse to give me an information unless I'm a contractor.
matt151617 is offline   Reply With Quote
Old 11-18-2011, 02:32 PM   #2
Rewards Points: 590
You can pull the wire to the LO (it's on a quick disconnect), but you would need to make sure your boiler is cold-start. Mine is, but it's also at least 12 years old and leaked a lot of condensation when I did that. I just leave it at that minimum 110 degree setting now.
operagost is offline   Reply With Quote
Old 11-18-2011, 03:11 PM   #3
Rewards Points: 162
I will do that then, thanks. I've been shutting off the boiler all together during the summer. I had the LO at 110 and it didn't fire at all when the hot water was in use, so that should work good.
Setting the reset "Curve" for a modulating boiler (modcon) mknmike HVAC 5 02-10-2011 11:37 AM
Burner always stops at LOW setting on L8124L pleasehelpmike HVAC 2 01-19-2011 08:22 AM
I Need a New Boiler. What do i need to know New Boiler Co Plumbing 0 10-23-2010 06:03 PM
Boiler w. Hydronic Air & Honeywell Aquastat DanA28 HVAC 1 01-08-2009 04:21 PM
Boiler Problems @ LowThermostat Setting Ron6519 HVAC 9 12-05-2008 05:54 AM