Diamond 80 furnace problem
Igniter lights, burners come on for about 5 seconds then the gas shuts off and of course burners go out. I power cycle the unit, same results. I am an Automotive Technician with Advanced electrical expirence so if anyone can give me a start, I would greatly appreciate it.
I was looking for a photocell of sorts but didn't see any.
P.s inducer motor runs continuously though, proving out the thermostat.
Thanks. Joe
Jej34 is offline   Reply With Quote
Old 04-23-2012, 06:34 PM   #2
Rewards Points: 582
start by cleaning flame sensor....
Old 04-23-2012, 06:37 PM   #3
Flame sense problem by the sounds of it. Is this a hot surface ignition (glowing coil) system or a spark ignition?
Edward12 is offline   Reply With Quote
Old 04-23-2012, 06:54 PM   #4
An old Tradesmen
Rewards Points: 7,356
Links to other DIY sites are not permitted.
The Following User Says Thank You to beenthere For This Useful Post:
Edward12 (04-23-2012)
Old 04-23-2012, 07:15 PM   #5
Is the flame sensor a photocell. All I see is what're appears to be a thermocouple on the left and 2 round metal sensors near the burner ports but they are just metal(nothing to clean)
Igniter is element type, not spark.
Thanks Men
Old 04-23-2012, 07:32 PM   #6
It is a hot surface ignition system. The" thermocouple" you are referring to should be a metal rod which may be the sensor. Try cleaning it as Ben's plumbing mentioned. Make sure you turn the power off, and be careful not to bump the igniter. Also make sure that the sensor is located directly in the flame. You should be able to see it good while the unit fires before it locks out.
Old 04-23-2012, 07:44 PM   #7
how
Rewards Points: 1,104
Is this a downflow model?? Just because of the York recall for that model in the downflow style...
Your flame sensor will usually be in front of the burner that is farthest away from the igniter. One sheet metal screw holding it in place.
A clean fine steel wool works well.
how is offline   Reply With Quote
Old 04-23-2012, 07:46 PM   #8
Not down flow. Found sensor, I'll clean it up and see.
Thx
Old 04-23-2012, 09:49 PM   #9
Cleaned it, working like a champ at the moment!
Thanks Men
The Following User Says Thank You to Jej34 For This Useful Post:
ben's plumbing (04-23-2012)
Heil Furnace Burner Problem timothyr HVAC 79 02-12-2014 07:01 PM
Help troubleshooting furnace problem robert_ HVAC 21 02-15-2012 08:04 AM
Help with furnace blower problem Spydey HVAC 6 12-15-2010 08:18 PM
Furnace Model # Feh-015-04 clicking but not turning on? haimei HVAC 1 12-14-2010 05:01 PM
Old Silver-Line furnace problem avro1 HVAC 9 03-18-2010 12:01 AM