Dead Furnace - HVAC - DIY Chatroom Home Improvement Forum
Old 01-27-2013, 02:00 AM   #1
Dead furnace
Hi,
I have a Consolidated Industries Model MBA 060 NH2R, Smart Valve is HW SV9500, control unit Model ST9141A1002, part # 406650.
I was connecting a new Filtrete 3M-50 thermostat and made the mistake of connecting the blue wire from the furnace to the B terminal instead of to the "C" terminal. The thermostat smoked a bit, so I quick ran to the panel turned off the power. After connecting it correctly, I turned on the breaker and now the furnace doesn't turn on at all. No light on the control unit, zippo. I tried connecting swapping thermostats with the one downstairs and the thermostat is undamaged.
Did I fry the control unit? Looking at the furnace wiring diagram, I don't see any other fuse or breakers that could have been blown or tripped.
After reading other posts on this forum about this furnace, it appears that this unit is a lemon and this control unit failing is quite common. The furnace is ~18 years old, so it could be time for the unit to fail. I just thought it was strange that connecting this wire incorrectly on the thermostat could fry the control unit, but I suppose it's possible.
Hopefully someone can confirm that this is possible. I found one online for $129. I may try to swap the control unit from the other furnace to confirm this is bad.
Thanks in advance for any help!
bonifp is offline   Reply With Quote
Old 01-27-2013, 07:12 AM   #2
An old Tradesmen
Rewards Points: 6,544
Probably burned out the transformer.
Old 01-27-2013, 11:29 AM   #3
Rewards Points: 1,294
I would agree with this. You realy need a volt/OHM meter to check everything out
danpik is offline   Reply With Quote
Old 01-27-2013, 01:52 PM   #4
90 percent sure is your transformer, on your control board check from R to C with a volt meter
And see what you get. If 0 volt , it's your
Transformer or your line voltage coming it.
ryandeen is offline   Reply With Quote
Old 01-27-2013, 03:01 PM   #5
Bingo! I swapped transformers with the other furnace and it fired right up. Now where to buy a replacement? It's a Basler BE26654003. Does Home Depot carry these? Local plumbing supply? I found one online for $19 but not sure I want to wait 3-4 days without heat.
Old 01-27-2013, 05:05 PM   #6
Experienced HVAC Tech
HVAC1000's Avatar
make sure it at least 40VA otherwise you will fry that one too.
http://www.homedepot.com/webapp/cata...gry=Search+All
here is one from the Home Depot that will work for you. just make sure you follow the directions for which wires to use on it
HVAC1000 is offline   Reply With Quote
Old 01-28-2013, 12:52 AM   #7
I was able to find the exact same model/PN so I should be good to go.
Thanks everyone for the help. You saved me lots of $$
Heil Furnace Burner Problem timothyr HVAC 79 02-12-2014 08:01 PM
Propane Furnace - Diminishing Gas Supply After Ignition edro HVAC 9 01-13-2012 05:24 PM
Furnace running proper? Spydey HVAC 6 12-16-2011 08:57 PM
Problem with Lennox Pulse Furnace Wiring to Thermostat scalvin Electrical 4 12-30-2009 08:48 PM
Olsen BFL 120 Furnace DaleB HVAC 12 12-19-2008 11:42 PM