Contactor Replacement Problem - HVAC - Page 2 - DIY Chatroom Home Improvement Forum
Old 06-07-2010, 05:22 PM   #16
New transformer and you should be good to go now. The wires, the way they were in the picture, were a direct short. That's why the transformer burnt out.
Old 06-07-2010, 09:18 PM   #17
An old Tradesmen
Rewards Points: 7,268
Originally Posted by Marty S. View Post
Can't tell for sure but it looks like the contactor has low voltage terminals on each side and you have both hooked to the same side. Are those terminals on the contactor right next to the capacitor?
Now that I look at it again. And for longer. Your right, the terminals are on both side of it.
Rick. Get a transformer with a resetable breaker.
Old 06-07-2010, 10:24 PM   #18
Would where I install the resettable breaker?
rickcusaf is offline   Reply With Quote
Old 06-07-2010, 10:27 PM   #19
An old Tradesmen
You get a transformer that has it built in already.
Old 06-08-2010, 01:04 PM   #20
Ok, I just installed a brand new transformer and still have no lights on the board.
Problem solved. I forgot to turn it on. =p