hi, i have a split system 2 ton ruud that heats and cools 3 rms upstairs. The inside unit is working when t-stat calls for heat or cool but the condenser unit does not come on. I checked power on the 2 yellow wires that hook to the contactor and showing 26 volts going in so i thought the contactor was bad being it is about 16 yrs old,and so ireplaced the contactor cost 11.00 dollars. But now i have the same problem 26 volts to contactor but not pulling in, BUT when i manually press the contactor down everything works fine, on heat or cool mode. Can someone help me out with what i should check next or other most logical causes......thanks
Marty S. 03-30-2010 05:50 PM
Double check the new contactor and make sure it's not a 120 volt coil. With 26 volts present it should pull in if it's the right contactor.
beenthere 03-30-2010 06:31 PM
Did you check voltage across the coil, or did you check it to ground?
oren 03-30-2010 08:37 PM
when i check from 24 volt side terminal to opposite side of contactor terminal (or Across the coil) i don't get any reading. But if i run a jumper wire from common on the control board to the terminal opposite the 24 volt terminal it makes the contactor pull in.....
Scuba_Dave 03-30-2010 09:15 PM
Why a 2nd login ?
beenthere 03-30-2010 09:44 PM
Then the contactors were both fine. And you have a problem with your wiring.
PS: use the contact us to get the password of your first account if you forgot.
Unless Dave knows another way.
oren 03-30-2010 09:45 PM
had'nt actually registered with the site when i first posted, when i did user name was already taken so i had to change it
beenthere 03-30-2010 09:55 PM
Both names are registered to you. And both are registered to the same IP address. And list the same email address.