Confused about AC CFM on varying Furnaces
IS there not a standard number, say 400 cfm, per ton for furnace developement for use with AC, per ton?
I ask because I saw this one, but it indicates it is good up to a 5 ton Ac, but only produces 1800 CFM. Seems low for 5 tons to me? http://www.alpinehomeair.com/viewpro...ctID=453065680 Comments, explanation? |
It'd be like a 5 ton blower on a lower speed setting. Since they don't make a 4.5 ton condenser (in half tons 3.5 is the biggest, then 4 and straight to 5) it's just a selling point that they say it is compatible and while it is it's not the best, correct match up.
You'll never get the full cooling parameters of a 5 ton system. |
Now if used with a heat pump than 350 cfm per ton is the common number so 1750 cfm would be all that's required, that would work with a 5 ton heat pump.
400CFM per ton is a nominal desired CFM. Many 5 ton systems only have 1600 to 1750 CFM of actual air flow.
I would stay away from the one you posted. Unless your duct system is ideal. The blower in it is rated at a max 1800CFM at a .5" ESP. So if your duct system is under sized like most, you may not even gt 1600 CFM through it. And have your A/C coil freeze up at mild outdoor temps, and a higher electric bill because of the bower motor running at its highest RPM. |
Thanks BT, no just looking. That caught my eye because I thought the rule of thumb was 400 square feet per ton.
| All times are GMT -4. The time now is 01:44 AM. |