Condenser Not Equalizing After Cycling Off - HVAC - Page 2 - DIY Chatroom Home Improvement Forum
Old 08-31-2014, 01:14 AM   #16
I'm Your Huckleberry
Rewards Points: 2,270
txv or any other metering device, filter drier and or valves.
Thanks.
Doc Holliday is offline   Reply With Quote
Old 08-31-2014, 08:06 AM   #17
An old Tradesmen
Rewards Points: 6,516
Originally Posted by a.man1302 View Post
If a system is not equalizing, is the TXV a good culprit? What else would cause this issue?
Balance port TXVs are not suppose to equalize. So swapping out a balance port TXV with another balance port TXV won't make it equalize.
Old 09-02-2014, 12:07 AM   #18
Rewards Points: 225
The TXV in question is not a balanced port type... Doc, when you said valves, did you mean the compressor valves?
a.man1302 is offline   Reply With Quote
Old 09-02-2014, 05:05 AM   #19
An old Tradesmen
If a TXV is not a balanced port, or hard shut off TXV. Then if it is preventing the system from equalizing. The system should run in or near a vacuum on the low side when it runs.
Old 09-05-2014, 07:05 PM   #20
Rewards Points: 380
It would seem odd that the valve works properly when the unit is running, but not when the unit is shut down, typically a bad valve stays bad all the time. Even the balanced port valves will typically equalize to within about 75 PSI. It would be nice to know exactly how much equalization does occur within 3-5 minutes.
HVACDave is offline   Reply With Quote
Old 09-05-2014, 09:54 PM   #21
Rewards Points: 225
do you mean 75 psi between high and low side?
Old 09-05-2014, 11:04 PM   #22
Rewards Points: 380
Yes, 75 PSI press difference between high and low is pretty standard for older valves, newer design valves are running around 35 PSI.
Old 09-05-2014, 11:09 PM   #23
Rewards Points: 380
A similar situation occurred when changing from an old orfice style coil to a new txv coil, we would sometimes have to add a hard start to get the unit to run correctly due to lack of equalization in off cycle making the unit start loaded instead of unloaded.
Old 09-06-2014, 11:41 AM   #24
Rewards Points: 338
yep happened to me. went to a more efficient txv coil and the compressor would only start if it had about 45 minutes to sit and equalize. anything less than that and it wouldn't kick on. added a hard start kit and has been running fine for several years.
NitroNate is offline   Reply With Quote
Any Issues: Old Condenser - New System? JulieMor HVAC 3 07-05-2012 08:57 PM
HVAC condenser shutting off after 1 min - short cycling DeltaDave HVAC 2 06-01-2012 09:56 PM
Carrier Condenser Unit Screwed? gimmes name HVAC 6 07-24-2011 08:05 AM
Goodman Fan Condenser Replacement Help bigjohnstud4200 HVAC 2 07-03-2010 02:54 PM
Condenser Fan Cycling Switch Replacement wirenut1110 HVAC 2 01-23-2010 10:29 AM