Condenser fan that is slow spinning
I have a condenser fan that is moving very slowly. I went straight to the cap and I believe that is the problem. The cap is a 45/5. The numbers read as follows:21/1.7 Let me know If I am correct on this.
sirweldalot is offline   Reply With Quote
Old 08-03-2014, 05:29 PM   #2
An old Tradesmen
Rewards Points: 7,414
That would be a bad/weak capacitor.
The Following User Says Thank You to beenthere For This Useful Post:
sirweldalot (08-03-2014)
Old 08-03-2014, 05:33 PM   #3
Rewards Points: 112
Thanks. I figured so.
Old 08-04-2014, 05:44 PM   #4
Rewards Points: 112
slow spinning condenser fan
I changed out the cap. and it is working fine. The subcool is 8 and the superheat is 30. Lowside saturation is 46 degree's 140 psi. High side is 305 and 132 degrees saturation. 410 refrigerant. I think the unit is low.
Old 08-04-2014, 06:50 PM   #5
Rewards Points: 72
Is the coil, condensor and filter clean?
digitalplumber is just a name for use here, I am not a plumber!
digitalplumber is offline   Reply With Quote
Old 08-04-2014, 06:54 PM   #6
Rewards Points: 112
Yes. The unit is working fine now after the new cap.
Old 08-04-2014, 06:55 PM   #7
Rewards Points: 112
Just seems a little low on refrigerant. Is it because of the high superheat?
Old 08-04-2014, 09:22 PM   #8
An old Tradesmen
At 140PSIG suction, it doesn't sound low. What was the indoor temp and humidity, and the outdoor temp when you took these measurements.
Old 08-05-2014, 05:26 AM   #9
Rewards Points: 112
The indoor temp. was 82 degree's when I arrived at the home. I changed the cap. and turned on the unit. The unit came on and waited about 15 min. before checking pressures. Outside temp. was 85 degree's. I did the sub-cool and superheat. Subcool was 8 degree's which fall's between 2-10. So I was taught. The superheat was 30 degree's ,which should fall between 10-20. I did not check humidity. I did check the filter/drier between each side and it was 3 degree's different,which I was taaught that it could be no more than 6 degree's. Thanks for the help.
Old 08-05-2014, 05:39 AM   #10
An old Tradesmen
A liquid line filter drier with a 3 degree delta across it is in need of replacement. Its too restricted. It should have no temp delta across it.
Carrier condenser fan spinning slow Evstarr HVAC 6 07-12-2012 11:38 PM
Byrant A/C Compressor fan spinning slow RBattaglia HVAC 3 06-12-2012 09:46 AM
Ceiling Fan Doing Weiird Stuff (Spinning Backwards, Running Slow...) bcorz Electrical 6 07-20-2011 02:35 AM
Condenser fan motor spinning slowly or not at all utbigrod HVAC 1 06-08-2011 09:00 PM
Goodman Fan Condenser Replacement Help bigjohnstud4200 HVAC 2 07-03-2010 01:54 PM