Old 06-09-2012, 06:29 PM   #1
Post
I recently changed my Condenser Fan Motor as the other one locked up right before vacation. The motor was a 1/10 HP and the only motor I could find locally with the same RPM was a 1/2 HP. The old fan was .7 Amps and thew new one is 3.5-4.0.
1--What if any effects will this cause on my AC unit?
2--Can this cause any issues with my home electrical panel?
Had a local company here in Houston do a system check up and he said nothing about the fan motor but this may not be part of the service. The guys had only been doing HVAC for 10mos.
Any help would be much appreciated.
glcarter is offline   Reply With Quote
Old 06-09-2012, 07:01 PM   #2
No problems at all motor won't be working very hard so should last a lot longer maybe use a little more electricity but probably not noticeable long as rpms are same and it fits should be good
firedave19 is offline   Reply With Quote
Old 06-09-2012, 09:12 PM   #3
An old Tradesmen
Rewards Points: 6,860
It will have a short life span. It needs to work against a load close to its rating/amp draw rating. Get the proper motor.
The Following User Says Thank You to beenthere For This Useful Post:
hvactech126 (06-09-2012)
Old 06-09-2012, 09:25 PM   #4
Thanks for the responses...
I was more worried about electrical load on house panel. I will research the fan motor and see if I can find something closer to the HP rating of the original motor.
Old 06-09-2012, 10:39 PM   #5
Under voltage and over amperage will shorten lifespan but pulling lower amps will not save ur money it will last long time
Old 06-09-2012, 11:05 PM   #6
An old Tradesmen
An under loaded PSC motor doesn't last long.
Download and read Fasco's motor facts.
Old 06-09-2012, 11:13 PM   #7
Don't have too 20 years experience tells me what works companies print that stuff to reduce liability so they can deny it was their fault
Old 06-09-2012, 11:22 PM   #8
An old Tradesmen
20 years means nothing.
The motor will have a short life span.
hvactech126 (06-10-2012)
Old 06-10-2012, 06:09 PM   #9
Gentlemen,
Since the money has already been spent, why not let the motor last as long as it can?
As long as the increased amperage doesn't put the unit's total ampdraw over 80 percent of the circuit breaker's amp rating, you will not have any problems in your panel. What size circuit breaker do you have, and what is the unit's minimum circuit ampacity (MCA)?
TopTechnician is offline   Reply With Quote
Old 06-10-2012, 06:31 PM   #10
An old Tradesmen
Originally Posted by TopTechnician View Post
Gentlemen,
Cause it really bites when the motor fails on a hot Sunday, and no replacement is available.
Old 06-10-2012, 07:00 PM   #11
Rewards Points: 616
beenthere is correct on this one......
carmon is offline   Reply With Quote
Old 06-10-2012, 07:21 PM   #12
If the new motor current is substantially higher than that of the old motor it may shorten the life of the contacts of the fan motor relay.
Are you sure about the current draw of the old (220v?) motor? It seems awfully efficient (44%) for a motor that small.
Old 06-12-2012, 06:10 AM   #13
Rewards Points: 1,216
Purchase a new motor that is like and kind to the defective motor. Same HP same Amp, same everthing or your looking for trouble like been said on a hot humid Sunday. Make sure you don't damage the fan blade and install it in the exact spot (height) on the fan shroud.
COLDIRON is offline   Reply With Quote
Tags
condenser fan motor , fan motor horsepower
Solar at the cottage? Tito1800 Home Theater 2 01-18-2012 02:30 PM
Making a waterproof/weatherproof enclosures for a network camera & its power hub snowfall Building & Construction 0 05-02-2011 10:14 AM
Wring for Lincoln Power Mig Welder vstoyko Electrical 17 01-15-2009 06:15 PM
safe way to add extension to power cord sil Electrical 7 10-18-2007 09:58 PM
Partial power on same fuse! joyjam Electrical 5 07-10-2005 10:23 PM