Condensate Only Drains When Blower Stops - HVAC - Page 4 - DIY Chatroom Home Improvement Forum
Old 04-05-2011, 10:03 AM   #46
Maybe you should try only one drain hooked up. There may not be enough air pressure to overcome the water in the trap the second drain. Try a screw in plug for the other drain and put a cap on where it connects to the main drain line.
I dont think you really need two drains.
Artco is offline   Reply With Quote
Old 04-06-2011, 09:28 AM   #47
I reinstalled the cleanout for the primary drain and capped the secondary drain. I opened up the panel to take a look at the coil again. I could see the inside of the coils by removing the plate at the tip of the "A". They appeared pretty clean, no dust or other visible obstructions.
Since temps have been so mild here, there haven't been many opportunites to run the A/C. So the pan was bone dry. The trap from the primary drain still had water in it. I'll report back when conditions are better suited to test.
One last thing: when the blower comes on, with the primary drain's cleanout removed, and the secondary drain uncapped, the air flow out the primary is much greater than the secondary.
sethmorgan is offline   Reply With Quote
Old 04-06-2011, 10:37 AM   #48
You may find that the trap has to be removed because when it is full of water the air pressure is not enough to push the water through it.
Without the trap there is not much air loss to worry about when cooling is on because condensate is flowing and restricting a lot of air loss in the condensate pipe.
It will not affect your units cooling capacity.
I do commercial hvac and on some carrier and other mfg. Units if the drain is upstream of the blower they do not want a p trap installed because of the restriction put on the drain.
Old 07-23-2011, 04:32 PM   #49
I just wanted to update this thread with the solution. According to the installation documentation for the evap coil regarding the condensate drain:
"A trap must be used when the coil is installed on the
return air side of the system. When coil is installed on
the supply side (outlet air) it is not necessary to install
a trap and better drainage is usually achieved without
the trap."
My coil is installed on the supply side, so I guess I need to remove the trap to resolve this. Thanks to all for the input.
Bryant Plus 90 - No Blower Ducaticorse HVAC 13 01-03-2015 05:39 PM
Heat comes on but blower never does aczer HVAC 12 02-13-2011 07:57 AM
Bryant Gas Furnace - blower sarts and stops montepix HVAC 7 12-24-2009 05:11 PM
Carrier 58MXA Wiring Blower Switch 63012753 HVAC 0 10-06-2009 10:09 PM
KNOWLEDGABLE condensate advice needed Nestor_Kelebay HVAC 5 11-23-2008 08:06 PM