Compatible HVAC System Question
I have recently had two HVAC techs install a completely new HVAC system and a new Ecobee Si. One of the guys wired the outside HP and one wired the indoor AH. I know that they had several of the wires wrong because I have checked them ex:
the B terminal at the HP was attached to a blue wire and that blue wire was attached to another blue wire which ran to the AH but the blue wire was not connected to anything inside or the D terminal at the HP (purple) attached to a black wire that ran to the AH and the black wire was attached to an orange wire that ran to the O/B terminal. I mentioned to one guy that he may need the instruction manual to the Ecobee since he has never installed one before. His reply was I can wire it with any wire, so its not a big deal I can do this in my sleep. It is a big deal if the other guy is using different wires!!! I can get the cool air to come on under the heat pump setting, but the heat only works if I have the furnace enabled and electric specified. I have been told by Ecobee that the AH and HP may not be compatible. There is no B or O terminal on the AH. The wiring diagrams in the manuals say that there is a B terminal on the AH, but the diagram that is on the AH itself does not have a B terminal. Is this correct? How should it be wired? I have no aux heat. currently it is wired as follows Thermostat -> AH -> HP W (O/B) - x - B Y - x - Y R - R - R C - C - C W2 - W1&W2 - D G - G Equipment rhsl-hm4221ja - Air handler 13pjl42a01 - 1 stage heat pump I can provide more information if needed. Thanks, Frank |
You do not have furnace.
AH and HP are Rheem..... so BS what the "guy" from Ecobe said. They can use any wires color to connect. Since this industry is a mess in reference to code. It's just not a good practice. |
you have no aux heat when? In Emergency heat mode? When the thermostat is set x degrees higher than the room temp?
It looks to be wired properly. I don't see a B terminal in your air handler wiring. Nor should the be one with a psc motor type air handler. http://www.natureaircorp.com/downloa...ng_diagram.pdf Is the thermostat setup for a heat pump with electric aux heat? |
I have no heat period when the thermostat is configured for 1 stage heat pump. To get heat I have to configure the thermostat to electric furnace. There is no aux heater installed. It is aftermarket and they did not install one. There also is no emergency heat.
I know you can use any wire "color" to connect but when one guy wires the b terminal and at the other end the other guy wires that to the d terminal there is a problem.
Here's the thing. Why would both the AH & HP manual have a diagram showing that there should be a B terminal to go from thermostat to ah to hp then the ah model they install not have one? Also all the research I've done online has the ah with a B terminal for proper function of a hp system.
The B terminal on your system is reversing valve function. The ahu does not need to see the RV signal on a psc motor ahu like you have. The ecobee must be setup for RV signal with heating. Pretty much All other manufacturers use RV signal with cooling.
I have made sure the settings regarding the reverse valve are correct.
| All times are GMT -4. The time now is 03:07 AM. |