There can be two sets of pressure contacts that could be closed.
1. the gas pressure?
2. the inducer/combustion pressure contacts ?
when you have a furnace that you rely on for safety and warmth and depend on it .
Among your family, it would be wise to have it checked out by a professional.
your life may depend on it.
Also, each time you power off the unit and restart it , you may be erasing the correct error fault code and resetting the furnace, and what oyu may be looking at is a code that might be something different???
Does the Furnace even ignite the or does it go to fault next time the furnace calls???
next time , after the furnace is reset, after it becomes satisfied at the thermostat, make it call for heat again at the t-stat.
then go watch the sequence of operation , see what happens.
does the induce/combustion small fan start up first, then the ignitor lights then the gas burners come on, then the blower fan motor?
or where does the furnace stop at which point? what was the last part of the sequence of operation? what came on last and then stopped prior to going into fault error code?
Thanks , wasn't sure if that was the code,,,, you posted in the middle of my posting.... good idea,,, it would be usually a good start, unless the stack has a blockage or the motor is bad??? inducer/combution...
i was uncertain with the pressure valve as the description of the error?