-   -   Comfortmaker RPJ - 1 Flash - Nothing ON (http://www.diychatroom.com/f17/comfortmaker-rpj-1-flash-nothing-5643/)
olgranddad 01-01-2007 12:59 PM
Hi all,
A lovely way to start the new year, the furnace goes out.
I have a Comfortmaker RPJ II Model GUI100A012BIN. I believe the house was built about 1994. This is the original furnace.
I am getting 1 flash which says its in lockout mode.
The ignitor does not heat up. There is no clicking for the flame.
Two weeks ago I cleaned the flame sensor and the furnace has worked fine until now. I replaced the filter in mid October.
I have power to the unit. If I turn the fan ON instead of AUTO it runs fine. I have shut down the system, rebooted it, and still don't have anything remotely trying to turn on.
I have held the lockout switch IN and received the 1 flash. It doesn't repeat the sequence.
Any ideas?
Thank You
trollmastergeneral 01-01-2007 02:10 PM
I would recomend putting on the bottom door shutting the power off at the disconet switch for 5 seconds and then restart furnace. Know I would watch what happens from there. report back:whistling2:
olgranddad 01-01-2007 02:23 PM
I have done that a number of times (5 seconds through 5 minutes). I have shut power down from the disconnect switch, as well as, from the breaker. I secure the lower panel and still nothing happens. The ignitor doesn't even start to warm.
#CARRIERMAN 01-01-2007 02:33 PM
Hi oldgrandad
If this unit has a Honeywell Smart Valve it sounds like this could be your problem. If it does the only way to repair the problem is to change the gas valve. But to make this determination. I would like for you to first check all limits and make sure you don't have one open. If you could be a little more detailed I could nail it down for you.
Good luck
Rusty
trollmastergeneral 01-01-2007 02:43 PM
Does this furnace have a ventor motor.it may be locking out because it tries three times and then lockes out.I dont think rpj has a ventor.
#CARRIERMAN 01-01-2007 02:49 PM
Hi trollmastergeneral
The Comfortmaker, Arcoaire, Heil, and Tempstars have used a inducer since the mid 80's. That about the time the government really cracked down on furnace efficency. And you could have just hit on the problem. It could be the pressure switch not making or could even be its not breaking the contacts.
olgranddad 01-01-2007 02:57 PM
I don't see a "Ventor Motor" on any of my documentation. I do see the "Induce Draft Blower" which is not operating. I see the shaft inside of the motor windings turn very slowly. I do see the "Supply Air Blower Motor" which operates when I put the Fan on ON instead of AUTO.
olgranddad 01-01-2007 03:09 PM
Originally Posted by #CARRIERMAN (Post 28426)
Hi oldgrandad
Good luck
Rusty
I see no mention of Honeywell anywhere on the gas valve.
I believe there is only one limit. It is to ensure the bottom panel is closed. The switch is working as when the fan is ON, it turns OFF as soon as the limit switch is OPENed by removing the panel.
Are there other limits I should be looking for?
olgranddad 01-01-2007 03:34 PM
Upon reading more...the manual says
"When the 120V power source is energized, the control module will flash once, indicating the system is ready for operation." THIS IS MY SINGLE FLASH
I don't have any flashes after that.
The manual then says "On a call for heat, the thermostat contacts close, signaling the control module". When I changed the thermostat target point from below to above the current temperature, I hear the contacts close.
Then the manual says "The control module continuously performs a self check routine. If at any time the control senses a failure, internally or externally, the indicator light will respond using the following code...."
Internal failure - Steady Light
External failure - Flashing Light
I never see a steady light nor a flashing light.
Then the manual says "The control module will check for normally closed contacts on the high limit and normally open contacts on the pressure switch. The system will then energize the induced draft blower, and purge for 30 seconds."
I do not see the furnace do this.
trollmastergeneral 01-01-2007 03:37 PM
Induced draft blower and ventor motor mean the same thing. If this is turning very slow it probably has a bad motor or you may find something like a bird or squrial in the motor assembly.Already taken out 2 this year myself. Shut off the power to furnace and carefully touch the vent motor if it is" hot "I would pull motor off and check it.
olgranddad 01-01-2007 03:44 PM
The motor is basement temperature. I was able to stop it from turning, but I had to turn the Fan/Blower OFF.
trollmastergeneral 01-01-2007 04:32 PM
I think there is some confusion here so I will try to straightn this out.There is a blower in the bottom of the furnace, this can be turned on manualy at the thermostat if it is wired in.The exhaust motor,ventor motor,or induced draft motor are all the same thing.this motor turns on when there is a call for heat.The purpose of this motor is to exhaust the fumes from the furnace. does the induced draft motor on yours come on? You will probaly have to have the top door of furnace off.make sure bottom door is on because there is a safety switch on this one.
olgranddad 01-01-2007 04:45 PM
The induced draft motor does not come on.
I did notice it was turning very slowly. The induced draft motor turns slowly when the blower is manually turned ON at the thermostat. Otherwise it does not turn at all.
The bottom door is on securely fully pressing the lock out switch. The blower will not turn if the lock out is not pressed. The blower will manually turn ON, so I assume the lock out is pressed.
Thank you for your responses and help :)
trollmastergeneral 01-01-2007 04:51 PM
If the induced draft motor does not spin up to speed the presure switch will not make allowing furnace to light can you check for voltage at the motor leads when there is a call for heat.
#CARRIERMAN 01-01-2007 05:02 PM
Hi oldgranddad
Trollmaster just hit the nail on the head. You have a bad inducer assy. If this motor does not come up to speed it will not make the pressure switch and will not allow the burners to come on. Some of them had oil ports on them, if your lucky you might be able to oil it and get through the night. Trollmaster good job.
Rusty
