Comfort Maker Gas Fired Furnace - HVAC - DIY Chatroom Home Improvement Forum
Old 03-30-2009, 06:56 PM   #1
cnw
Question
Just finished installing new motor,set thermostat to "auto" and "heat",burners came on ,but not the blower motor,put fan in "on" mode with a call for heat,blower motor operates with burners for approximately one minute,then the motor stops running,but the burners contine firing,blower motors operates fine in"on "mode without a call for heat,works fine in "auto"/cool mode.Anybody have any idea what's going on
cnw is offline   Reply With Quote
Old 03-30-2009, 07:01 PM   #2
Hvac Pro
yuri's Avatar
Rewards Points: 1,102
Sounds like you may have crossed up some wiring for the heat speed or have poor connections somewhere. Putting it in ON energizes the motor thru the cooling relay. Was it an identical motor or a universal type. Post the model and serial # of the furnace.
Old 03-30-2009, 07:02 PM   #3
GC/Master Plumber/Mech
Rewards Points: 560
How long did you wait after the burners come on to see if the blower will come on?
The heat exchange has to get hot and make a limit close to turn on the blower anywhere from 5 to 10 minutes.
Also if you can post model
Old 03-30-2009, 07:08 PM   #4
Hvac Pro
yuri's Avatar
Just trying to help plumber101 and the OP, FYI all the new furnaces with circuit boards are timed on for the fan and it usually is after 45 seconds or they would overstress the heat exchanger. The old bi-metal jobs took a long time, usually 3-5 minutes but gave you nice roasty heat.
Cheers
Old 03-30-2009, 07:10 PM   #5
cnw
Question
I waited for what semed to be approximately five minutes,I wired the new motor the same way the OEM motor was wired,noted location of each wire upon disconnecting,but will do a double check,the model number is:
GNI060A012BIN/serial number L93055211,Where can one get a wiring diagram or troubleshooting guide for this furnacs?
Old 03-30-2009, 07:24 PM   #6
Rewards Points: 560
Can you post a pic or post wire colors and to which terminal you made the connection?
Old 03-30-2009, 07:34 PM   #7
Hvac Pro
yuri's Avatar
Wiring diagram should be on the back of the fan door. Pics will help.
http://www.gocomfortmaker.com/go/index.asp?t=86&s=477
Have to dig for the manual. That old unit may have a heater/timed on fan control made by Camstat which may be faulty and not a full blown modern circuit board. Post some pics of the burner area.
Old 03-30-2009, 07:59 PM   #8
cnw
Question
Wil try and get some pics on Wednesday and double check wiring,etc.There wasn't a wiring diagram on the door as usual.Tried searching info on the web address posted,but only goes back to 1998,believe this unit is much older,I remember when I had to purchae an inducer motor kit,it was $248.00,and the distributor commented on it's age.
Old 03-31-2009, 12:48 AM   #9
check for 120v at fan heat speed term and neutral during heating cycle. if none exsists, and you changed the blower because of the problem you described, you likely have a bad board and replaced the blower for nothing
kennzz05 is offline   Reply With Quote
Old 03-31-2009, 12:52 AM   #10
limits are always closed and open upon sensing too much heat
limits do not control the fan cycle other than turning it on upon an overheating condition and turrning off the heating source gas/oil
Old 03-31-2009, 08:00 AM   #11
HVAC / Plumbing
He can also connect 110 to the blower terminals when disconnected form the board to check motor.. it the motor runs forever it's not blower motor.. Mabe has burn out low speed windings.In cooling mode you are on either med or high speed if you have 3 speed motor
kenmac is offline   Reply With Quote
Old 03-31-2009, 12:16 PM   #12
An old Tradesmen
Rewards Points: 6,088
May be the old motor wasn't bad either.
I'd test the old motor if you still have it.
If it works, well, you have a spare now.
And know to look at other possible problems.
Old 03-31-2009, 07:25 PM   #13
Rewards Points: 560
Thanks Ken and Yuri but I assumed this had a fan/limit. Ya know Limit closed and fan open
I figured it may that old and not have a delay on on the board
But you know what happens when you ass-u-me
comfort maker mnopytfbc HVAC 10 03-18-2009 03:28 AM
Help - Problem with Oil Fired Forced Air Furnace JohnF HVAC 13 01-31-2009 10:04 PM
Problems with new furnace..Overheating, having to reset. Furnace too big? Tommy2 HVAC 41 12-01-2008 02:55 PM