We are installing a Patriot 80 oil burner in a 16x14x7 basement room, and running the return through an adjoining room that is 12x24x7 to the upstairs level of the house. How much combustable air should be needed for the unit, and if more is needed from the adjoining larger room, what size hole would be needed to vent the proper amount of combustable air to the unit? There has to be a way to determin the amount of combustable air in a room, and likely how much that the unit requires that may not be in the owners manual.
Lee Roy is offline   Reply With Quote
Old 10-26-2010, 04:34 PM   #2
HVAC / Plumbing
Originally Posted by Lee Roy View Post
proper amount of combustable air to the unit? .
I would not want any. You want fresh air for appliance combustion
kenmac is offline   Reply With Quote
Old 10-26-2010, 06:32 PM   #3
Need 50 cubic feet of free air for every 1000 BTU including the water heater. One way is to put grill on the walls connecting rooms, one within 12" of the ceiling and one within 12" of the floor. There's a formula for how much air can pass through 1" grill space but I can't rember it right now. One of the other guys will know shortly. Got to have more supply feeding these rooms then return or the negative pressure can make the flue downdraft.
As kenmac stated the other option is to bring it in from outside. Again can't recall the exact procedure but believe it's no less then half the flue diameter. Down side is it makes a mighty cold room in the winter which will freeze pipes if you don't have enough heat blowing in there.
Old 10-26-2010, 06:55 PM   #4
Hvac Pro
yuri's Avatar
Rewards Points: 1,424
He would have to know the oil burner nozzle size and firing rate and convert that to BTU's, not easy. Best to just put a louvered door into the furnace room and allow the air into the house naturally. That way there is no cold drafts in the furnace room etc. Oil burners are power burners/fan assissted and can easily draw air in thru a louvered door. If he seals the house airtight then he may have chimney problems etc and needs additional outside combustion air. Most homes are leaky enough not to have that problem.
Old 10-26-2010, 07:08 PM   #5
Thanks yuri. A quarter million people in and around town and I work on exactly one oil burner. Thought they were purchased like gas furnaces with a specific BTU for the house needs.
Old 10-26-2010, 07:12 PM   #6
Hvac Pro
yuri's Avatar
The older ones could use 3 different nozzle sizes. Newer ones are more house size specific but he would still need all that info to know for sure.
Old 10-26-2010, 07:24 PM   #7
An old Tradesmen
Rewards Points: 6,544
Between those 2 rooms. You have enough volume for 71,680 BTUs of input.
So what size is your furnace?
The Following User Says Thank You to beenthere For This Useful Post:
Lee Roy (10-27-2010)
Old 10-27-2010, 01:07 PM   #8
The unit says 85000 BTU's, we have weatherized the upper part of the house, really tightened things up from what they were. We ran the return through a cinderblock wall, and now I am framing the hole. My plan is to use two 20x24 inch grates to allow air flow between the rooms. I can also add a smaller one to allow outside air if needed. What is the formula used to determin combustable air and BTU ratio? My local hardware store said they just use a chart. Thanks for your help.
Old 10-27-2010, 07:21 PM   #9
An old Tradesmen
50 cubic foot per 1,000 BTUs of input.
Then what you lack. You need to add 4 sq in per 1,000 BTUs.
So a 6" pipe is all you would need to add from the outside.
Old 10-27-2010, 11:17 PM   #10
One thing they allow here when a little short on combustion air for replacement jobs is to put in a gutted 4x10 supply in the room. Has to have a sticker applied stating "combustion air- do not cover". Won't fly on new construction though.
Size of whole house fan needed Doug Crf General DIY Discussions 20 02-26-2011 12:29 AM
no ductwork needed to install a wall fan ? amakarevic Plumbing 2 01-22-2010 06:23 PM
Wire Needed for GF / Arc Fault breaker jamiedolan Electrical 13 09-20-2009 09:15 AM
calculating amount of exhaust vents needed bitty071203 HVAC 4 06-09-2009 08:13 PM
Help on materials needed for granite tile c4m4r0 Flooring 4 06-02-2007 03:05 PM